i have old air handler capacity 5 ton 10 seer and i want to change the existing condensing unit that is 5 ton 10 seer with a 4 ton 13 seer.

is that going to work? and if not what is the problem with it?

Posted

It is going to work? Hard to say, you might get lucky. Is it proper to install a 4 ton condenser on a 5 ton coil without changing the orifice or TVX on it? Absolutely not. What about using a 13 SEER condenser on a 10 SEER air handler? Nope. It's a lousy gamble with your money. Do it right.

The 4 ton has a lower refrigerant flow rate than the 5 ton. And a 4 ton 13 SEER likely has a lower refrigerant flow rate than a 4 ton 10 SEER. The 13 SEER's have larger condenser coils, smaller compressor capacity but same tonnage when joined to a matching inside unit. Your evaporator (cooling) coil will be starved for refrigerant, resulting in inadequate head pressure, bubbles in gas, reduce cooling capacity (from 4 tons), etc.

Marc

Posted

The first thing you should do is have someone do a Manual J calculation so you know what size your house really needs. There is no need to guess on unit size when calculations will give you the correct answer.

Posted

Out of curiousity, does anyone on this forum actually complete Manual J calculations as an inspector?

I'm thinking of buying the ACCA Manual D and Manual J books and learn how to do these two calculations because I'm seeing lots of lousy duct system installations on new construction and I suspect that the tonnages aren't the best choice either.