I have a client that is selling his home in another state and moving here. His buyer's inspector called out the S-Trap below. My client wants to know if it is something worth fighting. He writes "my understanding is if they have a trap arm length greater than 2 pipe diameters between the p-trap and vertical limb, then they really aren't S traps. The pipe diameter in the p-trap is 1.5 inches. The length of the trap arm is 3.5 inches. I believe the other inspector is right in that it is an S trap and should be fixed and what the client is talking about is trap arm lengths to vent. I just need some clarification/feedback before I answer.

Thanks.

Click to Enlarge
tn_201041372949_Picture1.jpg

25.38 KB

Click to Enlarge
tn_201041373014_Picture2.jpg

32.5 KB

Posted

We can't tell from that pic if it is an S or not. The trap arm length references the distance to the vent, so if the arrow in the pic points to a Tee then it is a P trap and Randy is correct, but if it's an Ell then the buyer's HI is correct. Either way it's wrong.

Click to Enlarge
tn_201041395129_TRAP.jpg

28.55 KB

Your client should be glad they only want the trap fixed. I'd want the hole in the wall repaired as well.

Tom

Posted

Fight what? You should tell your client it's wrong and that he should write his buyer a check for a couple hundred bucks and get on with his life. Let the new buyer hire a real plumber to make it right.

PS. Whenever I see a trap with no cleanout, I just know there's more trouble nearby.

Posted

It's not an s-trap but it's still wrong. The vent opening in the wall is below the weir of the trap. It must be above.

Installing a longer tailpiece down from the sink will solve the problem.

ditto!