Hello All,

I know that I have some pretty lame brain questions sometimes so why should this be any different? [:-dunce]

Is it possible to tell visually if a unit has an economizer or not without opening the unit and looking inside at the damper?

I have included a few rooftop package unit examples.

Click to Enlarge
tn_201046103437_A.jpg

44.89 KB

Click to Enlarge
tn_201046103533_B.jpg

42.09 KB

Posted

The short answer is no Joe.

You can have o/a dampers that are just used for 10% makeup/fresh air into the building.

If you are writing a report, and need to verify the presence of an economizer, you really should pull a panel to look and also have a peek at the wiring diagram/control logic.

Posted

If it is cool outside but warm in the building, it opens the damper further thereby using the outside air as cooling instead of using the compressor.

Also called "Air side Economizer" or "Free Cooling"

The compressor may be turned completely off completely or "partially left on" for dehumidification in some instances and control schemes .

Considering your last post about cleaning calipers in closed systems, I think you are just pulling my leg about forgetting what that is though. [:-thumbu]

Cheers