Jim Katen Posted December 14, 2009 Report Posted December 14, 2009 Erik, 7 feet for a hot tub disco is code compliant. So 680.41 does not apply? No. That section doesn't apply to single family dwellings. - Jim Katen, Oregon
Erik Posted December 14, 2009 Report Posted December 14, 2009 http://www.neca-neis.org/cqd/index.cfm? ... on&id=2921
Jim Katen Posted December 14, 2009 Report Posted December 14, 2009 To a large degree, Randy's right. I never see the stuff you're talking about. The only thing I see is conduit in all it's forms. This NM stuff has me baffled. So let me get this straight........the problem is UF in conduit(?). THWN is correct(?). Sure. The problem is that UF isn't one of the approved wiring methods for this situation. Neither is EMT, by the way. The fact that it's "protected" by conduit doesn't matter. Would THHN be OK? That would depend on the location. If this were a dry or damp location, THHN would be fine. But it sounds like the conduit is in a wet location. If so then the interior of the conduit is also considered a wet location and you'd have to use wires that had the letter W printed on them somewhere. That said, I can't see why a length of UF inside conduit would be a problem in this case. I know it doesn't comply with 680.21. It just doesn't feel like a rightous call in this case. What rational is at work here? - Jim Katen, Oregon - Jim Katen, Oregon
Jim Katen Posted December 14, 2009 Report Posted December 14, 2009 http://www.neca-neis.org/cqd/index.cfm?fuseaction=showArchiveQuestion&id=2921 And your point? The information in that link does not support your assertion that a disconnect 7' away from the spa is a problem. - Jim Katen, Oregon
Erik Posted December 14, 2009 Report Posted December 14, 2009 Service switch not less than five feet?
Jim Katen Posted December 14, 2009 Report Posted December 14, 2009 Service switch not less than five feet? Yes. That means that the switch has to be *more* than 5' away from the inside walls of the spa. If the switch is 7' away, that's good. It complies. - Jim Katen, Oregon
kurt Posted December 14, 2009 Report Posted December 14, 2009 How 'bout LFMC, or LFNC? Sealtight? I know I said "conduit", but I wasn't thinking EMT, I was thinking waterproof flex. I understand how it's not right, but in this case, does it really matter other than to show off super fine tuned-ness? I mean, what possible thing could go wrong other than Jeff being the AHJ and making you change it? FTR, I'd have never found that in a million years.......
Jeff Remas Posted December 14, 2009 Author Report Posted December 14, 2009 Erik, 7 feet for a hot tub disco is code compliant. So 680.41 does not apply? 680.41 does not apply because this is a SFR. The disconnect is 7 feet away and within site so it is not an issue.
Jeff Remas Posted December 14, 2009 Author Report Posted December 14, 2009 Service switch not less than five feet? Yes Erik with a K, NOT LESS THAN therefore it needs to be 5' or MORE away from the hot tub. The link you posted above does not apply because this is a SFR and the answer in the link does not qualify SFR. Most of these jobs are with PVC and THWN pulled inside. I just did a job for my aunt like this 2 weeks ago. I pulled NM inside the house and from the exterior disco to the hot tub I pulled THWN, 6/3NM inside the house and #8 THWN outside the house and was able to maintain the 50A required rating..
electures Posted December 23, 2009 Report Posted December 23, 2009 *Hot tub installed outdoors. *50A GFCI breaker in main panel inside the home. *6/3 NM runs inside the home and terminated inside a properly placed disconnect within site of the hot tub. *From the disco 6/3 UF is properly protected and runs to the hot tub. All wiring is correct and the hot tub functions. Is there a problem with this install? Sorry for the late post, but I just joined. NM cable is permitted inside the dwelling only. The disconnect is outside.
electures Posted December 23, 2009 Report Posted December 23, 2009 Service switch not less than five feet? Yes Erik with a K, NOT LESS THAN therefore it needs to be 5' or MORE away from the hot tub. The link you posted above does not apply because this is a SFR and the answer in the link does not qualify SFR. Most of these jobs are with PVC and THWN pulled inside. I just did a job for my aunt like this 2 weeks ago. I pulled NM inside the house and from the exterior disco to the hot tub I pulled THWN, 6/3NM inside the house and #8 THWN outside the house and was able to maintain the 50A required rating.. NEC 110.14©(1)(a)(1) states; (a) Termination provisions of equipment for circuits rated 100 amperes or less, or marked for 14 AWG through 1 AWG conductors, shall be used only for one of the following: (1) Conductors rated 60°C (140°F). #8 is rated 40A @ 60C
electures Posted December 23, 2009 Report Posted December 23, 2009 OK, now that I have your attention, lets break this down. What run is in violation?: 1) The NM from the main panel to the disconnect 2) The UF from the disco to the hot tub 3) Both runs We have to determine what the "branch circuit" is. 1) NM is a violation as stated in my previous post. 2) UF is also a violation. 680.40 General. Electrical installations at spas and hot tubs shall comply with the provisions of Part I and Part IV of this article. 680.25 (B) states; (B) Grounding. An equipment grounding conductor shall be installed with the feeder conductors between the grounding terminal of the pool equipment panelboard and the grounding terminal of the applicable service equipment or source of a separately derived system. For other than (1) existing feeders covered in 680.25(A), Exception, or (2) feeders to separate buildings that do not utilize an insulated equipment grounding conductor in accordance with 680.25(B)(2), this equipment grounding conductor shall be insulated.
Jeff Remas Posted December 24, 2009 Author Report Posted December 24, 2009 Service switch not less than five feet? Yes Erik with a K, NOT LESS THAN therefore it needs to be 5' or MORE away from the hot tub. The link you posted above does not apply because this is a SFR and the answer in the link does not qualify SFR. Most of these jobs are with PVC and THWN pulled inside. I just did a job for my aunt like this 2 weeks ago. I pulled NM inside the house and from the exterior disco to the hot tub I pulled THWN, 6/3NM inside the house and #8 THWN outside the house and was able to maintain the 50A required rating.. NEC 110.14©(1)(a)(1) states; (a) Termination provisions of equipment for circuits rated 100 amperes or less, or marked for 14 AWG through 1 AWG conductors, shall be used only for one of the following: (1) Conductors rated 60°C (140°F). #8 is rated 40A @ 60C You left out this part: (3) Conductors with higher temperature ratings if the equipment is listed and identified for use with such conductors. (4) For motors marked with design letters B, C, or D, conductors having an insulation rating of 75°C (167°F) or higher shall be permitted to be used, provided the ampacity of such conductors does not exceed the 75°C (167°F) ampacity.
Jim Port Posted December 24, 2009 Report Posted December 24, 2009 NM into the back of the disco is fine. This is no different than having NM feed an exterior light or receptacle when coming into the back of the box. This would not be considered an exterior.
electures Posted December 24, 2009 Report Posted December 24, 2009 NM into the back of the disco is fine. This is no different than having NM feed an exterior light or receptacle when coming into the back of the box. This would not be considered an exterior. 680.21(A)(4) is specific and states; (4) One-Family Dwellings. In the interior of dwelling units, or in the interior of accessory buildings associated with a dwelling unit, any of the wiring methods recognized in Chapter 3 of this Code that comply with the provisions of this section shall be permitted. Where run in a cable assembly, the equipment grounding conductor shall be permitted to be uninsulated, but it shall be enclosed within the outer sheath of the cable assembly. 680.3 states; 680.3 Other Articles. Except as modified by this article, wiring and equipment in or adjacent to pools and fountains shall comply with other applicable provisions of this Code, including those provisions identified in Table 680.3. No where in 680 does it permit NM cable outside the dwelling. Also, 680 has nothing to do with outside lighting fixtures and receptacles in any other area except the pool.
electures Posted December 24, 2009 Report Posted December 24, 2009 Service switch not less than five feet? Yes Erik with a K, NOT LESS THAN therefore it needs to be 5' or MORE away from the hot tub. The link you posted above does not apply because this is a SFR and the answer in the link does not qualify SFR. Most of these jobs are with PVC and THWN pulled inside. I just did a job for my aunt like this 2 weeks ago. I pulled NM inside the house and from the exterior disco to the hot tub I pulled THWN, 6/3NM inside the house and #8 THWN outside the house and was able to maintain the 50A required rating.. NEC 110.14©(1)(a)(1) states; (a) Termination provisions of equipment for circuits rated 100 amperes or less, or marked for 14 AWG through 1 AWG conductors, shall be used only for one of the following: (1) Conductors rated 60°C (140°F). #8 is rated 40A @ 60C You left out this part: (3) Conductors with higher temperature ratings if the equipment is listed and identified for use with such conductors. (4) For motors marked with design letters B, C, or D, conductors having an insulation rating of 75°C (167°F) or higher shall be permitted to be used, provided the ampacity of such conductors does not exceed the 75°C (167°F) ampacity. That means all terminations including wirenuts.
Jim Katen Posted December 25, 2009 Report Posted December 25, 2009 NM into the back of the disco is fine. This is no different than having NM feed an exterior light or receptacle when coming into the back of the box. This would not be considered an exterior. 680.21(A)(4) is specific and states; (4) One-Family Dwellings. In the interior of dwelling units, or in the interior of accessory buildings associated with a dwelling unit, any of the wiring methods recognized in Chapter 3 of this Code that comply with the provisions of this section shall be permitted. Where run in a cable assembly, the equipment grounding conductor shall be permitted to be uninsulated, but it shall be enclosed within the outer sheath of the cable assembly. 680.3 states; 680.3 Other Articles. Except as modified by this article, wiring and equipment in or adjacent to pools and fountains shall comply with other applicable provisions of this Code, including those provisions identified in Table 680.3. No where in 680 does it permit NM cable outside the dwelling. Nor does it prohibit it. The first section you quoted just says that, in the interior, X is permitted. That's not a prohibition. This is not the section that you want to quote to support your argument. If you want to argue against NM running into an outdoor disconnect box, you might avoid stating that NM is only allowed inside a dwelling. That's really hard to back up. Instead, I'd concentrate on 334.12(B)(4). It prohibits NM in wet or damp locations. Armed with that prohibition, you could say that the NM shouldn't run to the disconnect box because the disconnect box is supposed to be mounted 1/4" away from the outside wall (312.2) and the NM would necessarily have to pass through that space. For the situation in the original post, I think your previous argument, citing 680.25(B), was spot on if there's a breaker in the disconnect box, but I think that most folks didn't catch it. That argument says that the cable that runs to the disconnect is, technically, a feeder (because it comes before the final overcurrent protection device). Because this is a hot tub, there are special rules for feeders that require their grounding conductor to be insulated. (With some exceptions that don't apply here.) - Jim Katen, Oregon
Jim Katen Posted December 25, 2009 Report Posted December 25, 2009 That means all terminations including wirenuts. Yes. And wire nuts are rated at 105 degrees C. Wire nuts are seldom the limiting factor in determining ampacity. - Jim Katen, Oregon
Jim Katen Posted December 25, 2009 Report Posted December 25, 2009 NM into the back of the disco is fine. Well, it's nearly a universal practice, but for pools & spas the EGC should be insulated if there's a breaker in the disconnect. And for things other than pools & spas there's still that pesky 1/4" air space that's considered a wet location. It's not the end of the world, I know, but it's still, technically, wrong. This is no different than having NM feed an exterior light or receptacle when coming into the back of the box. This would not be considered an exterior. There are actually two differences. First, the disconnect box is surface mounted, while the light & receptacle boxes are recessed. Second, the disconnect serves a spa, which brings in a whole set of requirments from Article 680 that wouldn't apply to most other exterior lights & receptacles. - Jim Katen, Oregon
electures Posted December 26, 2009 Report Posted December 26, 2009 NM into the back of the disco is fine. This is no different than having NM feed an exterior light or receptacle when coming into the back of the box. This would not be considered an exterior. 680.21(A)(4) is specific and states; (4) One-Family Dwellings. In the interior of dwelling units, or in the interior of accessory buildings associated with a dwelling unit, any of the wiring methods recognized in Chapter 3 of this Code that comply with the provisions of this section shall be permitted. Where run in a cable assembly, the equipment grounding conductor shall be permitted to be uninsulated, but it shall be enclosed within the outer sheath of the cable assembly. 680.3 states; 680.3 Other Articles. Except as modified by this article, wiring and equipment in or adjacent to pools and fountains shall comply with other applicable provisions of this Code, including those provisions identified in Table 680.3. No where in 680 does it permit NM cable outside the dwelling. Nor does it prohibit it. The first section you quoted just says that, in the interior, X is permitted. That's not a prohibition. This is not the section that you want to quote to support your argument. If you want to argue against NM running into an outdoor disconnect box, you might avoid stating that NM is only allowed inside a dwelling. That's really hard to back up. Instead, I'd concentrate on 334.12(B)(4). It prohibits NM in wet or damp locations. Armed with that prohibition, you could say that the NM shouldn't run to the disconnect box because the disconnect box is supposed to be mounted 1/4" away from the outside wall (312.2) and the NM would necessarily have to pass through that space. For the situation in the original post, I think your previous argument, citing 680.25(B), was spot on if there's a breaker in the disconnect box, but I think that most folks didn't catch it. That argument says that the cable that runs to the disconnect is, technically, a feeder (because it comes before the final overcurrent protection device). Because this is a hot tub, there are special rules for feeders that require their grounding conductor to be insulated. (With some exceptions that don't apply here.) - Jim Katen, Oregon I think 680.21(A)(4) is clear enough. Once the building envelope is pierced and the NM cable enteres the disconnect, it is outside the building. Weather it is 1/16" or 16", it is outside. Enough said. "Nor does it prohibit it". Since 680.21(A)(4) clearly reads interior how could that be interpreted any other way?
electures Posted December 26, 2009 Report Posted December 26, 2009 Service switch not less than five feet? Yes Erik with a K, NOT LESS THAN therefore it needs to be 5' or MORE away from the hot tub. The link you posted above does not apply because this is a SFR and the answer in the link does not qualify SFR. Most of these jobs are with PVC and THWN pulled inside. I just did a job for my aunt like this 2 weeks ago. I pulled NM inside the house and from the exterior disco to the hot tub I pulled THWN, 6/3NM inside the house and #8 THWN outside the house and was able to maintain the 50A required rating.. NEC 110.14©(1)(a)(1) states; (a) Termination provisions of equipment for circuits rated 100 amperes or less, or marked for 14 AWG through 1 AWG conductors, shall be used only for one of the following: (1) Conductors rated 60°C (140°F). #8 is rated 40A @ 60C You left out this part: (3) Conductors with higher temperature ratings if the equipment is listed and identified for use with such conductors. (4) For motors marked with design letters B, C, or D, conductors having an insulation rating of 75°C (167°F) or higher shall be permitted to be used, provided the ampacity of such conductors does not exceed the 75°C (167°F) ampacity. 110.3(B) reads; (B) Installation and Use. Listed or labeled equipment shall be installed and used in accordance with any instructions included in the listing or labeling. The UL White Book reads; NONMETALLIC-SHEATHED CABLE (PWVX) USE This category covers Types NM-B and NMC-B nonmetallic-sheathed cable, rated 600 V, intended for use in accordance with Article 334 of ANSI/NFPA 70, ââ¬Ëââ¬ËNational Electrical Codeââ¬â¢Ã¢â¬â¢ (NEC), and Listed in copper sizes 14 to 2 AWG inclusive and aluminum or copper-clad aluminum sizes 12 to 2 AWG inclusive. This cable contains conductors rated 90°C; however, the ampacities of the cable are those of 60°C conductors as specified in Article 334 and Table 310.16 of the NEC. ALthough NM cable is constructed using 90C conductors, the ampacities shall be 60C. #8 NM cable is rated 40A. Period.
Jim Katen Posted December 26, 2009 Report Posted December 26, 2009 . . . I think 680.21(A)(4) is clear enough. Once the building envelope is pierced and the NM cable enteres the disconnect, it is outside the building. Weather it is 1/16" or 16", it is outside. Enough said. 680.21(A)(4) is clear, but it doesn't say what you want it to say. It simply saying that, in the interior of a dwelling, X is permitted. It doesn't say what's not permitted and it doesn't say what is or isn't permitted outside a dwelling. This section does not support your argument. Enough said. "Nor does it prohibit it". Since 680.21(A)(4) clearly reads interior how could that be interpreted any other way? Because it doesn't contain any prohibition. - Jim Katen, Oregon
Jim Katen Posted December 26, 2009 Report Posted December 26, 2009 Service switch not less than five feet? Yes Erik with a K, NOT LESS THAN therefore it needs to be 5' or MORE away from the hot tub. The link you posted above does not apply because this is a SFR and the answer in the link does not qualify SFR. Most of these jobs are with PVC and THWN pulled inside. I just did a job for my aunt like this 2 weeks ago. I pulled NM inside the house and from the exterior disco to the hot tub I pulled THWN, 6/3NM inside the house and #8 THWN outside the house and was able to maintain the 50A required rating.. NEC 110.14©(1)(a)(1) states; (a) Termination provisions of equipment for circuits rated 100 amperes or less, or marked for 14 AWG through 1 AWG conductors, shall be used only for one of the following: (1) Conductors rated 60°C (140°F). #8 is rated 40A @ 60C You left out this part: (3) Conductors with higher temperature ratings if the equipment is listed and identified for use with such conductors. (4) For motors marked with design letters B, C, or D, conductors having an insulation rating of 75°C (167°F) or higher shall be permitted to be used, provided the ampacity of such conductors does not exceed the 75°C (167°F) ampacity. 110.3(B) reads; (B) Installation and Use. Listed or labeled equipment shall be installed and used in accordance with any instructions included in the listing or labeling. The UL White Book reads; NONMETALLIC-SHEATHED CABLE (PWVX) USE This category covers Types NM-B and NMC-B nonmetallic-sheathed cable, rated 600 V, intended for use in accordance with Article 334 of ANSI/NFPA 70, ââ¬Ëââ¬ËNational Electrical Codeââ¬â¢Ã¢â¬â¢ (NEC), and Listed in copper sizes 14 to 2 AWG inclusive and aluminum or copper-clad aluminum sizes 12 to 2 AWG inclusive. This cable contains conductors rated 90°C; however, the ampacities of the cable are those of 60°C conductors as specified in Article 334 and Table 310.16 of the NEC. ALthough NM cable is constructed using 90C conductors, the ampacities shall be 60C. #8 NM cable is rated 40A. Period. Um, dude, no one is saying otherwise. Of course NM is always rated at 60 degrees. You don't have to go to the white book for that, it's right there in 334.80. Read Jeff's comment again. He used #6 NM indoors and #8 THWN outdoors. As long as all of the connection points are rated for 75 degrees, his installation is fine. - Jim Katen, Oregon
electures Posted December 27, 2009 Report Posted December 27, 2009 . . . I think 680.21(A)(4) is clear enough. Once the building envelope is pierced and the NM cable enteres the disconnect, it is outside the building. Weather it is 1/16" or 16", it is outside. Enough said. 680.21(A)(4) is clear, but it doesn't say what you want it to say. It simply saying that, in the interior of a dwelling, X is permitted. It doesn't say what's not permitted and it doesn't say what is or isn't permitted outside a dwelling. This section does not support your argument. Enough said. "Nor does it prohibit it". Since 680.21(A)(4) clearly reads interior how could that be interpreted any other way? Because it doesn't contain any prohibition. - Jim Katen, Oregon Um "Dude", Let me get this right. You are stating that since the NEC doesn't read that "NM cable is prohibited" it is acceptable to install NM cable outside the dwelling unit to the disconnect. However, the NEC clearly reads that NM cable is permissible "in the interior of dwelling units". Your argument is absurd. What code book are you looking at?
Jim Port Posted December 27, 2009 Report Posted December 27, 2009 Your interpretation of interior is the most rigid I have seen. I have yet to see an code inspector have an issue with NM into the back of a disco. What would you propose, a splice box on the inside of the wall and switch wiring methods? Where do you see as the limit of the interior; is it the face of the drywall or the vinyl siding?