Brandon Whitmore Posted September 29, 2009 Report Posted September 29, 2009 I inspected a manufactured home today. It was installed in 2007, but is yet to be lived in. I admit that I don't spend nearly as much time studying up on manufactured home installations as I do site built, so I have some questions. OR's building code for manufactured homes is here, for anyone interested: http://www.bcd.oregon.gov/programs/mdpr ... 02mds.html 1)I've noticed that on the last couple of manufactured homes I've looked at (both newer), there is only GFCI protection within 6' of a water source in the kitchen. I can't seem to find anything specifying where GFCI protection is required-- anyone know where I can look? ANSWER: 3280.806 Receptacle outlets. (a) All receptacle outlets shall be: (1) Of grounding type; (2) Installed according to section 210ââ¬â 7 of the National Electrical Code (NFPA No. 70ââ¬â1993). (3) Except when supplying specific appliances, be parallel-blade, 15-ampere, 125-volt, either single or duplex. (b) All 120 volt single phase, 15 and 20 ampere receptacle outlets, including receptacles in light fixtures, installed outdoors, in compartments accessible from the outdoors, in bathrooms, and within 6 feet of a kitchen sink to serve counter top surfaces shall have groundfault circuit protection for personnel. Feeders supplying branch circuits may be protected by a ground-fault circuitinterrupter in lieu of the provision for such interrupters specified above. Receptacles dedicated for washer and dryers, also located in a bathroom, are exempt from this requirement. 2)The front door threshold sticks up 2 1/4" above the interior floor surface. I can't find anything in the code listed above that specifies the max. threshold lip. I'm sure this is wrong, and would like to cite the 1.5" rule, but would like some back up. Even if I get documentation showing that this is ok, I will still mention that I think it's a trip hazard. 3)The skirting installed is James Hardi panel siding material. They ran it directly in contact with the ground at landscape and hardscape areas. This is wrong per the manufacturers installation instructions, so I would guess that it is technically not allowed by the manufactured housing code. I vaguely remember reading something about this in the code listed above, but haven't found it yet. This is from James Hardie: Can I use Hardipanel as skirting material on a mobile home? A: Yes. However it needs to be installed in accordance with our written installation instructions for Hardipanel siding in regard to framing, joints, paint and installation above ground. 4)There is no cold water shut off valve at the water heater-- is one not required? Any help for the above questions/ concerns would be greatly appreciated.
hausdok Posted September 29, 2009 Report Posted September 29, 2009 Jeez, Some of you guys don't even explore what's in here, do you? Go to "Library" on the menu bar above and then click on downloads. Then scroll down to the federal manufactured home code. OT - OF!!! M.
Brandon Whitmore Posted September 29, 2009 Author Report Posted September 29, 2009 Thanks Mike, I forgot that was in here [:-paperba I've got questions 2 and 4 answered.... (first post updated)
Brandon Whitmore Posted September 29, 2009 Author Report Posted September 29, 2009 Mike, While searching the downloads I noticed that this is no longer a functional link: Alternatives For 2-Wire (Ungrounded) Receptacles
hausdok Posted September 30, 2009 Report Posted September 30, 2009 Hi, I've deleted it. OT - OF!!! M.
patt Posted September 30, 2009 Report Posted September 30, 2009 Brandon 1. You're better off going directly to the HUD site (http://www.access.gpo.gov/nara/cfr/wais ... 80_08.html) if you're going to look up the construction standards. HUD does not update the standards on a fixed schedule like most building codes but whenever they feel the need to. The section you quoted 3280.806 references the 93 NEC but the current HUD standards references the 2005 NEC; § 3280.806 Receptacle outlets. (a) All receptacle outlets shall be: (1) Of grounding type; (2) Installed according to Article 406.3 of the National Electrical Code, NFPA No. 70ââ¬â2005. 2. HUD references the AAMA standards for windows and doors. 3. Skirting is not covered by the HUD standards, 4. § 3280.609 Water distribution systems. (b) Water outlets and supply connections (1) Water connection. â⬦ When a master cold water shutoff full flow valve is not installed on the main feeder line in an accessible location, the manufacturerââ¬â¢s installation instructions shall indicate that such a valve is to be installed in the water supply line adjacent to the home. â⬦
patt Posted September 30, 2009 Report Posted September 30, 2009 AAMA Standards fot MHs It's in these standards that you'll find the size requirements for egress windows (5 sf) and sill height (36"). You will not find them in the HUD standards. MOBILE & MANUFACTURED HOUSING COMPONENTS Voluntary Standard for Utilization in Manufactured Housing for Primary Windows and Sliding Glass Doors This performance standard sets the requirements for primary windows and sliding glass doors used in manufactured housing. The requirements contained herein are intended to set a reasonable performance standard that is acceptable to fulfill the requirements for primary windows and sliding glass doors within the manufactured housing industry. 1701.2-02 ................................................. Download ââ¬â $25.00 (Member Price: $10.00) ......................................................... Paper ââ¬â $50.00 (Member Price: $20.00) .............................................................. CD ââ¬â $55.00 (Member Price: $25.00) Voluntary Standard for Utilization in Manufactured Housing for Swinging Exterior Passage Doors Contains general requirements, testing and certification procedures, materials and methods, and construction requirements for swing exterior passage doors used in mobile and manufactured housing. Revised 10/02. 1702.2-02 ................................................. Download ââ¬â $25.00 (Member Price: $10.00) ......................................................... Paper ââ¬â $50.00 (Member Price: $20.00) .............................................................. CD ââ¬â $55.00 (Member Price: $25.00) Voluntary Standard Egress Window Systems for Utilization in Manufactured Housing General installation, operational and appurtenance requirements; test methods; and reports and certification for egress window systems. 1704-01 ................................................. Download ââ¬â $25.00 (Member Price: $10.00) ......................................................... Paper ââ¬â $50.00 (Member Price: $20.00) .............................................................. CD ââ¬â $55.00 (Member Price: $25.00)
Brandon Whitmore Posted September 30, 2009 Author Report Posted September 30, 2009 Peter, Thanks. A single conversation with a wise man is better than ten years of study. ~Chinese Proverb