Brandon Whitmore Posted September 7, 2009 Report Posted September 7, 2009 Does anyone have a copy of installation instructions from say around 1996 for fiber cement siding joint treatment requirements? If not, how about a more recent copy that shows that caulk is not required at the joints? Thanks
Jim Katen Posted September 7, 2009 Report Posted September 7, 2009 Does anyone have a copy of installation instructions from say around 1996 for fiber cement siding joint treatment requirements? If not, how about a more recent copy that shows that caulk is not required at the joints? Thanks I don't have anything from 96. Here are the current instructions. Check figure 2. Download Attachment: install_plank_west.pdf 1239.4 KB
Brandon Whitmore Posted September 7, 2009 Author Report Posted September 7, 2009 The reason I ask; an appraiser is requiring that the butt joints be re- caulk sealed on a house built back in 1996. The siding is butted tightly, and then caulked. As always, the caulk has failed due to the lack of an adequate gap. The appraiser will be doing a re- inspection once the sealant touch- up has been done. I'm kinda wondering if it's his way of making some extra cash by requiring a re- inspection. The Realtor called me to find out whether this was odd, and I told her that while caulk is a good idea, I'm not so sure it was originally required.
patt Posted September 7, 2009 Report Posted September 7, 2009 Hardiplank 2001 Download Attachment: Hardie plank 2001.pdf 249.58 KB NER report 2000 Download Attachment: ner 405 Hardi 2000.pdf 350.42 KB
James_Hardie Posted October 1, 2009 Report Posted October 1, 2009 In 1996 and for years afterward James Hardie recommended that plank be butted in moderate contact, or, gapped an 1/8â€
Brandon Whitmore Posted October 2, 2009 Author Report Posted October 2, 2009 Thanks James_Hardie, Do you guy's keep a library of all of your past installation instructions by chance? If so, I'd love to add them to TIJ's library for future reference.
Ken Meyer Posted May 10, 2012 Report Posted May 10, 2012 Reviving an old thread here. Brandon, were you ever able to find any older Hardie Plank installation instructions? The oldest ones I have are from 2007. I'd like to know how if a 1/4" uncaulked gap between siding and horizontal flashing was required back then. Thanks
Brandon Whitmore Posted May 11, 2012 Author Report Posted May 11, 2012 Hi Ken, If you look at Peter's post above, you will see some from 2001. What year are you looking for?
Brandon Whitmore Posted May 12, 2012 Author Report Posted May 12, 2012 Wow-- back in the beginning...... I never got an entire set of instructions like I wanted. I did find this PDF from Certainteed that references a bunch of 1990's standards from ASTM: http://www.cookcountylumber.com/pdfs/specialty_products/certainteed/architecturalspec.pdf
Brandon Whitmore Posted May 12, 2012 Author Report Posted May 12, 2012 I'd like to know how if a 1/4" uncaulked gap between siding and horizontal flashing was required back then. According to James_Hardie's comment above, they recommended moderate contact or a gap with caulk from the beginning.......
patt Posted May 12, 2012 Report Posted May 12, 2012 . I'd like to know how if a 1/4" uncaulked gap between siding and horizontal flashing was required back then. 2005 was the first year that the instructions for Hardiplank specifically required an un-caulked 1/4" gap above horizontal flashing. First printing was in September 05 with an effective date December 05. Maintain a 1/4" clearance between James Hardie products and horizontal flashing (fig. 6). Click to Enlarge 15 KB Download Attachment: hardiplank install eff 12-05.pdf 604.71 KB
Ken Meyer Posted May 12, 2012 Report Posted May 12, 2012 Thanks Brandon and Patt, I was able to find the 2000 and 2005 instructions, but nothing older. The 2000 does not show the uncaulked gap. What made me wonder is that above the windows in the photos you can see the gap, but it has been re caulked by the homeowner. Other windows on the house look like they have original caulk, or at least someone did a neater job. There are 2 west facing second story windows that had problems likely from weather exposure; rain and baking late afternoon sun, and from lack of maintenance. The fix that was done on both windows was a heavy application of caulk, including covering the weep holes for good measure. There was some rot on vertical trim, I scanned the interior wall adjacent to one of the windows with a moisture meter but didn't find anything. The other room had a bed blocking the window. So my question is: what would your recommendation be for caulking above these windows when repairs are done; leave the gap above the windows uncaulked as current installation instructions say, or follow the guidelines from when the siding was originally installed? Click to Enlarge 36.03 KB Click to Enlarge 43.53 KB Click to Enlarge 42.54 KB
Brandon Whitmore Posted May 13, 2012 Author Report Posted May 13, 2012 The flashing is run short at the ends and to make matters worse, it appears to slope back towards the wall. I'd recommend opening the weep holes back up and caulking the heck out of everything. I'd be hesitant to recommend the removal of caulk when it may be all that is keeping the water out of the wall.....
hausdok Posted May 13, 2012 Report Posted May 13, 2012 You can see the outline of the upleg of the head flashing on the siding above the window where the paint is peeling. Since I've never seen that with HP before, I suspect that it doesn't extend behind the WRB behind the siding. If it doesn't extend behind the WRB, it wasn't working anyway and caulking the gap probably didn't help much and didn't make it any worse. ONE TEAM - ONE FIGHT!!! Mike