kurt Posted January 29, 2009 Report Posted January 29, 2009 New construction house; builder proposes insulation method..... 1) 2x6 wall cavity 2) plans on spraying in 1" of closed cell foam on interior side of sheathing. 3) followed by R19 batts, which will of course, end up compressed. Anyone heard of this? The supposed benefit is getting the increase R value (1"=approx. r6 + r19 = approx. r25). I'm researching, but am interested in opinions (other than "whadda goofy f***ing idea").
hausdok Posted January 29, 2009 Report Posted January 29, 2009 Hi Kurt, Unless it's a high-density batt, an R19 batt is sized to fully fill a 2 by 6 cavity. If he blows in an inch of closed cell, he'll compress the batting an inch and reduce it's R-value by roughly 3.55, which will result in a wall of only 15.45 + 6 or R21.45. He'll come closer if he uses an R15 high-density 3-1/2inch batt and two inches of closed cell. ONE TEAM - ONE FIGHT!!! Mike
kurt Posted January 29, 2009 Author Report Posted January 29, 2009 That's what my quick head calc says too. When he told me what they planned, I just sort of blanked. I'd never heard or seen of such a thing. That's why I'm asking. There's no benefit other than air barrier, no? I don't know why they don't go all foam. That's tomorrows conversation......
randynavarro Posted January 29, 2009 Report Posted January 29, 2009 It's gotta be a cost thing. In fact, installing that batt insulation may cause problems as there will be gaps between the back of the batt insulation and the spray foam. Air gaps on the warm side of a vapor barrier in a cold climate is trouble.
kurt Posted January 29, 2009 Author Report Posted January 29, 2009 Another good point. The guy is a good guy, and he's honestly trying to do "right" by his (and my) client, but he's in over his head. He's trying to satisfy the clients request for "lots of insulation". This is one of those where i wish I'd been included at an earlier stage.
hausdok Posted January 29, 2009 Report Posted January 29, 2009 Hi, The advantage to the closed-cell foam is that it will stop more air movement than insulation; so, you might get an R25 but you end up with a wall that costs energy wise like a leaky wall with R30 or better batting. I'm not so certain that you'd get condensation on the back of the FG with an inch of foam there. first, he really wouldn't need a vapor barrier because of the foam and, unless the temp at the face of the foam is low enough to cause condensation, I don't think it's going to be an issue. If the foamer does a good job and the wall is properly draft sealed, the warm air migrating in there should be enough to keep the foam warm enough to avoid condensation. Two inches would be better, but one might work fine. It's becoming pretty common to use a 1-inch layer of foam on the undersides of roofs and then use unfaced batting below it in unvented catedral ceiling roofs, so it might work fine. ONE TEAM - ONE FIGHT!!! Mike
Chad Fabry Posted January 29, 2009 Report Posted January 29, 2009 Unless it's a high-density batt, an R19 batt is sized to fully fill a 2 by 6 cavity. If he blows in an inch of closed cell, he'll compress the batting an inch and reduce it's R-value by roughly 3.55, which will result in a wall of only 15.45 + 6 or R21.45. He'll come closer if he uses an R15 high-density 3-1/2inch batt and two inches of closed cell. Hi Mike, from what I understand compressing the R19 batt is essentially the same as turning it into a high density batt. There will be a loss from the compression, but not the full R3.5 loss that one would expect. They'd save money and get the same gains ( in my mind) by just detailing with foam and installing the VP directly behind the interior wall plane.
Jeremy Posted January 29, 2009 Report Posted January 29, 2009 What Randy said. R-21 batts are not much more costly than R-19. Properly detailed construction will not leak much air, and R-21 would perform as well as the proposed idea, without the concern of a double vapor barrier. Foam is a lot more costly and is probably the reason for the idea posted.(Trying to get the best of both worlds) In my opinion there would be no benefit, but possible trouble. Use one system or the other.
randynavarro Posted January 29, 2009 Report Posted January 29, 2009 Some wise-ass use to say: "Unconventional things behave unconventionally. . . "
kurt Posted January 29, 2009 Author Report Posted January 29, 2009 All excellent points. Thats' my nervousness. Mixing up systems makes it unconventional, and projecting how it's going to perform is guesswork. I'm going to push for one system or the other.
Jeremy Posted January 29, 2009 Report Posted January 29, 2009 I have R-21 in 6" walls with R-48 blown overhead, built in 08 and it's been very reasonable to heat. If I want to make changes or modifications later, I don't have to deal with the foam mess. I think if I were going to foam, I would consider going all the way and do the whole house with ICF's instead of conventional framing. Maybe next time.
hausdok Posted January 29, 2009 Report Posted January 29, 2009 Originally posted by Chad Fabry Unless it's a high-density Batt, an R19 batt is sized to fully fill a 2 by 6 cavity. If he blows in an inch of closed cell, he'll compress the batting an inch and reduce it's R-value by roughly 3.55, which will result in a wall of only 15.45 + 6 or R21.45. He'll come closer if he uses an R15 high-density 3-1/2inch batt and two inches of closed cell. Hi Mike, from what I understand compressing the R19 batt is essentially the same as turning it into a high density batt. There will be a loss from the compression, but not the full R3.5 loss that one would expect. They'd save money and get the same gains ( in my mind) by just detailing with foam and installing the VP directly behind the interior wall plane. Hi Chad, I don't actually know what the loss in total R-value would be by compressing insulation an inch or so. What I do know is that R-value is supposed to be dependent on the amount of trapped air that you have in the insulation; and, that since air is never really trapped in fiberglass insulation - just sort of slowed down as it tries to pass through - it seems to me that there's no way that a layman can accurately guess. Therefore, in my mind it makes sense to deduct the full 3.55 you'd get by losing an inch of insulation. I figure that if they want accuracy, they can install a high-density batt that's not as thick and they'll have the manufacturer's lab testing to back them up. I still don't think that you're going to see moisture condense in that wall. After all, if you wouldn't have seen condensation take place in a conventionally insulated wall with nothing but plywood or OSB for sheathing covered by Tyvek or some other type of polyolefin barrier, why would you have condensation on the inner face of closed cell that's eliminated all telltale drafts and has moved the inside face of that outside wall further into the heated zone? ONE TEAM - ONE FIGHT!!! Mike
kurt Posted January 29, 2009 Author Report Posted January 29, 2009 My largest thought is it's an increase in cost (foam), but not necessarily any increase in performance. Put the money where it counts, right? Secondary concern, is what could go wrong? While possible, I'd put condensation way down the list.
gtblum Posted January 29, 2009 Report Posted January 29, 2009 Originally posted by kurt While possible, I'd put condensation way down the list. Why? My biggest question about closed cell has always been, about condensation. How does moisture dissipate? What about the difference between the indoor and outdoor climate?
Jeremy Posted January 29, 2009 Report Posted January 29, 2009 Sounds like an experiment to me. The manufactures might like to know the outcome of this one.
Jeremy Posted January 29, 2009 Report Posted January 29, 2009 Originally posted by gtblum Originally posted by kurt While possible, I'd put condensation way down the list. Why? My biggest question about closed cell has always been, about condensation. How does moisture dissipate? What about the difference between the indoor and outdoor climate? The moisture can't dissipate, but if the cavity is full of closed cell there is no place for the condesation to take place. There is no air to condensate moisture from, or very little anyway.
Tom Raymond Posted January 30, 2009 Report Posted January 30, 2009 Sounds like a dangerous experiment to me, tell the builder to try it on his own house and let us know how it turns out. If they still insist on mixing systems, they would be better served with advanced framing and foam sheathing, and a little spray foam for added air sealing. I say let the manufactures and engineers do the experiments, they actually gain something from the money spent regardless of the outcome. Tom
jimmy Posted February 21, 2009 Report Posted February 21, 2009 foam or batt only ive done insulation for 20 years and depending on the foam it can cause condensation