This metal conduit feeds an A/C unit.

It is not bonded to the panel nor is there a grounding conductor.

Is this too-obviously incorrect or am I missing something?

Click to View

tn_20091818422_DSC04057.jpg

64.95 KB

Click to View

tn_200918184249_DSC04060.jpg

38.11 KB

Posted
Originally posted by Jeff Remas

That looks like a painted metal LB to me.

Are you referring to the bushing in the top photo? If so, it's plastic.
Why does the conduit have to be bonded?

Doesn't all conduit have to be bonded?

Posted

The conduit is the "bond". The metal pipe connecting everything is the grounding path.

If there's plastic anywhere, or a loose coupling, or any similar condition that breaks continuity, there's no ground path.

Posted

No riddle, I thought this was common knowledge.

An LB is the conduit body that connects the conduit and has a cover on it. The LB conduit body creates a pull point. You took the cover off of it to take a picture. That is the LB.

Posted

OK. Got it. Thanks.

I've never personally used EMT except for some cool art projects. I've only used and inspected romex. I don't do commercial. Every once in a while I'll inspect the work of an ambitous soul who's upgraded his garage with some EMT.

I briefly perused all my electrical manuals on my shelf and there's no reference to "LB." Is it tradesman jargon?

Now to the lack of grounding . . . the A/C unit needs a grounding conductor back to the main panel, no?

I seem to recall past discussions something to do with compressor motors being double insulated or something so "grounding" is not needed. I'm sure I'm not recalling that accurately.

Posted
Originally posted by randynavarro

This metal conduit feeds an A/C unit.

It is not bonded to the panel nor is there a grounding conductor.

Is this too-obviously incorrect or am I missing something?

Yes the air conditioner needs to be grounded, as does the conduit. If that's a plastic conduit body, then there should be an equipment grounding wire in there.

However, I agree with Jeff. It looks very much like a cast metal LB with grey paint on it. It even looks like there's bright metal in the lower tapping where you removed the screw. But you were there, and as I said, if it's plastic then it's wrong.

An LB is a pulling ell with the outlet in the Back. LLs have the outlet to the Left and LRs have the outlet to the Right.

- Jim Katen, Oregon

Posted
Originally posted by energy star

Pic #1 in post 13 is a wonderful display of planning.

Yeah that was a bad install. However, you should see the overhead from the pole to where they chose on the building. Horrible planning.

Posted

Service ell or pulling ell is a common term around here. The only folks that I know that call them LL's, LR's, or whatever, are home inspectors. Everyone that actually works with them calls them service ells and designates a size.

Does anyone else notice the sudden shift to acronyms on the boards? Katen made a funny joke about it over @ the ASHI board that almost no one got.

Is it the new "code" language for us?

Posted

I've always called them "LB" or "SLB" (for short LB).

The new code buzz word is "luminaire" instead of "light fixture".

FYI - Out of curiosity I used an ohm meter to see if a bunch of romex clamps on the side of a main panel were grounded or not.

That is the panel was painted and I was curious as to if the clamps were breaking through to the metal on the panel and thus were grounded or not.

Many were not conducting through to the metal and thus were "floating" (were not grounded).

So it is a good thing to use bonding bushings at the panel! (Not on romex clamps of course.)

Posted
Originally posted by kurt

Does anyone else notice the sudden shift to acronyms on the boards?

Is it the new "code" language for us?

Hope not. Acronyms are great when everyone knows what you're talking about. Can't learn much when you're confused by them.
Posted
Originally posted by gtblum

Originally posted by kurt

Does anyone else notice the sudden shift to acronyms on the boards?

Is it the new "code" language for us?

Hope not. Acronyms are great when everyone knows what you're talking about. Can't learn much when you're confused by them.

There is a difference in the acronyms showing up on message boards and the "official" acronyms for trade related parts. From an inspectors standpoint, I think it is beneficial to know parts by both.

Posted
Originally posted by Billy_Bob

I've always called them "LB" or "SLB" (for short LB).

The new code buzz word is "luminaire" instead of "light fixture".

FYI - Out of curiosity I used an ohm meter to see if a bunch of romex clamps on the side of a main panel were grounded or not.

That is the panel was painted and I was curious as to if the clamps were breaking through to the metal on the panel and thus were grounded or not.

Many were not conducting through to the metal and thus were "floating" (were not grounded).

So it is a good thing to use bonding bushings at the panel! (Not on romex clamps of course.)

I believe NEC adopted luminaire 2002.