Yesterday inspecting new construction, I found four receptacle outlets that did nothing on my SureTest...a blank screen. So I got out the trusty old three light tester and it told me there was an open neutral.

I can't find anything in my SureTest instructions that identifies open neutrals.

Any comments?

Posted

An open neutral is simply an incomplete circuit and will show up as a blank indicating an improperly wired or dead circuit. I'm not sure tht the other tester could tell the difference between an open hot or neutral could it?

Posted

Paul,

I've seen that happen on my inspectors Sure Test. I have the older ST-1D unit and mine will show an open neutral.

This is only one reason I haven't bought one of the newer Sure Test. Why should I have to carry around a three light tester to tell me about an open neutral?

Donald

Posted

Thanks for the comments!

I only recently started using the Sure Test after January's ASHI convention. So I have the three light tester in my pocket all the time. Basically I use the three light tester and fall back to the Sure Test when things start looking suspicious.

Posted

Paul...me too, but I also find the "newer" SureTest I have especially handy in older homes, circa 1920 and before. Boot-leg grounds, 20%+ voltage drops, you name it.

Sure glad those prior Sure-Test posts convinced me to buy a new "valuable" tool.

Posted

I purchased a Sure Test back in Feburary or so and attached it to the tool belt. I still use the little three light, faster cheaper, but the sure test saves a lot of time in those two story masonry houses where the receptacles appear to be grounded.

Posted

I actually use my Sure-Test first and only use my three light tester as a second opinion. The three light tester will not tell you about a false ground. If you're only testing a few receptacles with a Sure Test then you could be missing false grounds or excessive voltage drops.

Donald

Posted

Hi Paul,

I have an ST-1D. No lights at all is supposed to indicate no juice on the hot conductor. With an open neutral or with a reversed hot and ground you'll have a left and a center light lit and the right light will be out. However, the SureTest will not identify "multiple" deficiencies, reversal of ground and neutral conductors nor detect two hot wires on a circuit, so maybe there is more going on there than just an open neutral.

ONE TEAM - ONE FIGHT!!!

Mike

Posted

Gotcha Mike,

I reported "wiring problems (possible open neutral)" and punted it back to the electrician. I was just surprised that the Sure Test treated it like a dead circuit with no suggestion of what the problem might be.

Posted

I have issues with the AFCI feature of my SureTest. Today I tested a 5 bedroom, under load, and only two breakers tripped. I find more often than not, at least one AFCI wont trip when I check them. I haven't heard of any definitive protocol for testing.