kurt Posted October 21, 2008 Report Posted October 21, 2008 OK, so I've got the builder arguing that they don't have to have soffit vents. Plenty of ridge venting but no soffit vents. Muni passed it. Muni is on the 2006 IRC. I've looked in R806.1-R806.3, and it only discusses soffit vents being necessary for roofs where the drywall is applied to the underside of the rafters, i.e., vaulted ceilings. Where's the statement about soffit vents for your basic attic?
Jim Katen Posted October 21, 2008 Report Posted October 21, 2008 Originally posted by kurt OK, so I've got the builder arguing that they don't have to have soffit vents. Plenty of ridge venting but no soffit vents. Muni passed it. Muni is on the 2006 IRC. I've looked in R806.1-R806.3, and it only discusses soffit vents being necessary for roofs where the drywall is applied to the underside of the rafters, i.e., vaulted ceilings. Where's the statement about soffit vents for your basic attic? There's no IRC requirement for soffit vents. They're just an option. - Jim Katen, Oregon
kurt Posted October 21, 2008 Author Report Posted October 21, 2008 That's what my take was, and honestly, I was kind of surprised. So, is there any basis for my insisting they be installed other than common sense and JLC?
Bain Posted October 21, 2008 Report Posted October 21, 2008 Did the builder satisfy the 1/150 ratio just using ridge vents? You might nab him on the "free area" thing.
kurt Posted October 21, 2008 Author Report Posted October 21, 2008 There's a couple of gable end vents that he used in the "calculation". The numbers work out. Problem is, it won't work, as we all know.
Bill Kibbel Posted October 21, 2008 Report Posted October 21, 2008 Might the shingle manufacturer require "balanced" ventilation?
hausdok Posted October 21, 2008 Report Posted October 21, 2008 Hi, You're right, it probably won't work but there's not a lot you can do to move an intransigent builder and/or muni. I normally just explain the issue to the client, tell the client that it's my opinion that it won't work and that I'll be writing it up that way, but not to expect the builder to do a whole lot about it, 'cuz it's been my experience that most builders and muni guys think that home inspectors like us are smokin' wacky tobaccy. I tell the client to insist on all of the answers from the builder and muni guy in writing, keep an eye on it if they buy it, and keep their litigation attorney on speed dial for the day that they discover that I was right and the builder and muni guy were wrong. ONE TEAM - ONE FIGHT!!! Mike
kurt Posted October 21, 2008 Author Report Posted October 21, 2008 Every authoritative source sez balanced venting. Just not the IRC.
Richard Moore Posted October 21, 2008 Report Posted October 21, 2008 Muni is on the 2006 IRC. I've looked in R806.1-R806.3, and it only discusses soffit vents being necessary for roofs where the drywall is applied to the underside of the rafters, i.e., vaulted ceilings.Where's the statement about soffit vents for your basic attic? R806.1 Ventilation Required. Enclosed attics and enclosed rafter spaces where ceilings are applied directly to the underside of roof rafters shall.... Kurt, I read that as "enclosed attics" and "enclosed rafter spaces" with the subsequent "ceiling applied directly to the underside of roof rafters" only applying to the bit after the "and". In other words, enclosed attics and/or cathedral ceilings are required to have ventilation. I agree that R806.2 doesn't require eave vents for any attic IF the the 1/150 rule is followed...but at least 20% would be for 1/151 to 1/300. Still stupid not to have it though.
Richard Moore Posted October 22, 2008 Report Posted October 22, 2008 So...if the average roof "mushroom" vent has a free opening of maybe 6"x6"(?), then a 1000sf attic would need 27 vents to meet the IRC 1/150 rule. Did you have that many? I'm not sure what the free area of the various continuous ridge vents is but the biggest I can find after a quick search online are 18 sq" per foot. 1000 sf attic would require 53 feet of that ridge venting (for 1/150).
Brian G Posted October 22, 2008 Report Posted October 22, 2008 Yep, another one of those common-sense items the code fails to nail down beyond the idiot of a doubt. What can you do? I've seen it a few times, and I tried to explain to my clients that what they would have is really just half a ventilation system; air outlets, but no air inlets. They seemed to get it okay, whether they actually did anything about it or not. Misson accomplished. Brian G. Thousands of Rules & Regulations, But an Idiot Will Find the Holes [:-irked]
randynavarro Posted October 22, 2008 Report Posted October 22, 2008 Then there's the rising tide of folks that argue for attics being air-tight. Seal 'em up and make 'em part of the conditioned space. Let's not go there right now.
kurt Posted October 22, 2008 Author Report Posted October 22, 2008 I'm one of those folks. In this case, though, the house is done and it can't be converted to conditioned space. This is just one of those stupid things that points out the stupidity of some aspects of the building code. If it was a steep pitch roof, or had big air space, I don't think it would be significant. As it is, the roof pitch is 4:12, and there's almost no air space up there. I've seen enough of these turn to mold farms that I think it's gotta have soffit vents. But, the guy will probably win because he's within "the law".
Chad Fabry Posted October 22, 2008 Report Posted October 22, 2008 Then there's the rising tide of folks that argue for attics being air-tight. Seal 'em up and make 'em part of the conditioned space. Let's not go there right now. I'm among that crowd. Kurt's example will be a moldy mess in short order. The best one can do in that case is what Kurt has done... educate the client. I inspected a rather large four square a few weeks ago. It was of the genre that includes a huge attic that could easily be converted to living space. For the last 105 years it's stood the test of time with no intentional ventilation but the roofer that last worked on the house studded the roofline with , get this, 11 box vents. It's truly lovely and one can stand at the top of the attic stairs and watch the door to the space strain to hold back the chimney effect. Open the door and it's like being in a trailer park in Alabama during tornado season. More venting is always better. Right?
Tom Raymond Posted October 22, 2008 Report Posted October 22, 2008 I know Randy asked us not go there but.... ...wrap your brains around this one guys, soffit vents cause ice dams. If this caused your head to explode don't blame me, the logic behind this conundrum comes straight from the mind of Joe Lstiburek. If I follow it right, a sunny exposure on a 30 F day will raise the wall temp to around 40 F (even warmer for dark colors), and this warms the air adjacent to the wall which then is boyant enough to rise through the soffit vents where it melts the snow on the roof deck from the bottom up. If the snow on the roof is deep enough to insulate the overhang the melt water running beneath it freezes at the eave, if not, it freezes as soon as the sun goes down. So why do we vent roofs like this? Tom
kurt Posted October 22, 2008 Author Report Posted October 22, 2008 Because ice dams can be dealt with by installing WR Grace; condensation in the attic on the underside of the roof deck cannot be dealt with except by vents. Or...... Completely rethinking how we insulate houses. I'm firmly in the icynene/no vents/condition the attic camp, although that could change if new information comes out contradicting what we thought yesterday. My own house is solid masonry, no soffit vents, decent insulation, and I still get major ice dams in sunny weather. Sunlight is gonna melt snow on the roof. Joe L. can think some of this stuff through too far, he's "right", but he's not right because this stuff boils down to a lesser of two evils thing. The problem isn't soffit vents, it's outdated insulation and building technologies prosecuted by completely untrained construction personnel. We're not going to change that, so vents will have to be used in some cases. In my case (yesterdays inspection), I'm saying gotta have soffit vents regardless. How the heck is it gonna stay dry inside otherwise? Plus, this house is 100 years old with a stone foundation and damp bsmt. conditions. Stack effect is gonna play havoc with the attic unless it's ventilated.
kurt Posted October 22, 2008 Author Report Posted October 22, 2008 Originally posted by Chad Fabry More venting is always better. Right? I'm pretty much at the point where I don't think old houses with big attics need much, if anything, in the way of venting. I see a couple hundred a year, and there's never a problem. Problems come with new OSB sheathing, new tight windows, or other improvements that change the vapor and air transmission rates in the structure. Your house (just described) didn't need vents. It was the untrained non-thinking installer that plugged in a standard formula.
Chad Fabry Posted October 22, 2008 Report Posted October 22, 2008 More venting is always better. Right? sarcasm is a funny thing. I didn't really mean that.
kurt Posted October 22, 2008 Author Report Posted October 22, 2008 I know that. I just don't feel like typing the report that's overdue and had to extemporize about anything other than what I should be doing.......
Les Posted October 22, 2008 Report Posted October 22, 2008 How is it that an old surfer hippie and a "click and clack" devotee use such big words?
hausdok Posted October 22, 2008 Report Posted October 22, 2008 Originally posted by Les How is it that an old surfer hippie and a "click and clack" devotee use such big words? They watch The Simpsons and King of the Hill a lot. ONE TEAM - ONE FIGHT!!! Mike
msteger Posted October 22, 2008 Report Posted October 22, 2008 I always use the 1/150 and 1/300 rules and think about uniform air flow from the soffits up to the ridge. I don't like gable vents, pan vents, or power fans as these can be counter-productive and may, in some circumstances, pull in warm air at the ridge, for example. I know Certainteed requires gable vents, pan vents, or power fans be removed, if ridge/soffit venting is added on a reroof (taken directly from their Master Shingle Applicator book). The other top manufacturers (Tamko, Owens Corning, GAF) highly recommend the same. I think IRC recommends soffits but doesn't require it. I would press the builder for soffit vents, and if you need to, use the shingle manufacturer's instructions and warranty paperwork to back you up.
kurt Posted October 22, 2008 Author Report Posted October 22, 2008 I love Hank Hill. I've gone over to Futurama on the other end; the Simpsons hasn't been funny for several years.
randynavarro Posted October 31, 2008 Report Posted October 31, 2008 Re-starting the discussion as I'm working on a rehab that needs attic ventilation. The language of R806.2 is certainly cumbersome if not downright confusing. Maybe it's just the day I'm having. The way I'm reading - eave or cornice venting is required if you're going to put 50% of the vents up high, no?
hausdok Posted November 1, 2008 Report Posted November 1, 2008 Hi Randy, Save yourself a headache and install a full-length ShingleVentII. Some frieze blocking vents, mesh and baffles and that thing will practically suck cars in off the highway. ONE TEAM - ONE FIGHT!!! Mike
Recommended Posts
Create an account or sign in to comment
You need to be a member in order to leave a comment
Create an account
Sign up for a new account in our community. It's easy!
Register a new accountSign in
Already have an account? Sign in here.
Sign In Now