John Dirks Jr Posted August 13, 2008 Report Posted August 13, 2008 A house has an attached garage. The access hatch(pull down stairs) in the garage is wood. The end wall in the garage attic between the house and garage is wafer board. Obviously, this is a concern for the spread of fire between the garage and house. Can one simply solve the problem by changing the access stairs to a hatch that uses proper fire rated gypsum, or, does one still need to cover the end wall with gypsum?
AHI in AR Posted August 13, 2008 Report Posted August 13, 2008 With a conventional single family home with the garage attached under the main roof, I'm not aware of any requirement for a fire-retardant wall in the attic between the home and the garage. I'd vote for adding proper fire retardant material over the pull down stair door.
John Dirks Jr Posted August 13, 2008 Author Report Posted August 13, 2008 Thanks Kevin. I see what you mean after I read the code. It says block between the garage and its attic space. R309.2 Separation required. The garage shall be separated from the residence and its attic area by not less than ½-inch (12.7 mm) gypsum board applied to the garage side. Garages beneath habitable rooms shall be separated from all habitable rooms above by not less than 5/8-inch (15.9 mm)
Tom Raymond Posted August 13, 2008 Report Posted August 13, 2008 I would be hesitant to advise "adding proper fire retardant material over the pull down stair door". There is more to a fire rated assembly than some gypsum over the hatch cover. FWIW, there are several very nice insulated and fire rated hatch systems out there, just don't expect to find them at your local lumber yard (forget even asking about one at the big box stores). Tom
John Dirks Jr Posted August 13, 2008 Author Report Posted August 13, 2008 That's a good idea Tom. Recommend the best and if they want to settle for less than it's their choice.
Tim H Posted August 14, 2008 Report Posted August 14, 2008 Originally posted by John Dirks Jr Thanks Kevin. I see what you mean after I read the code. It says block between the garage and its attic space. R309.2 Separation required. The garage shall be separated from the residence and its attic area by not less than ½-inch (12.7 mm) gypsum board applied to the garage side. Garages beneath habitable rooms shall be separated from all habitable rooms above by not less than 5/8-inch (15.9 mm) Seems pretty straightforward to me, but when I call out ( in the Birminham, AL area) no separation the AHJ says no problem. Many of these homes are less than 10 years old, and I have not seen a single builder of one of these newer homes that installs gypsum board to separate garages from the habitable rooms above. Todays inspection was different only in that holes were cut in the subfloor so that the plumber could install a garden tub. [:-paperba Am I missing something in this code section? Image Insert: 53.69 KB Image Insert: 51.64 KB Thanks, Tim
Bill Kibbel Posted August 15, 2008 Report Posted August 15, 2008 Tim, If those are pictures of a garage ceiling, I'm completely shocked. (Wrong ducts too) If the AHJ sez that's fine, I think you need to have a little press party. Invite newspaper and TV reporters to a new house and give 'em a little lesson on how it's supposed to be.
Tim H Posted August 15, 2008 Report Posted August 15, 2008 Originally posted by inspecthistoric Tim, If those are pictures of a garage ceiling, I'm completely shocked. (Wrong ducts too) If the AHJ sez that's fine, I think you need to have a little press party. Invite newspaper and TV reporters to a new house and give 'em a little lesson on how it's supposed to be. Bill, Yep, those are two different garage ceilings (common to see flex ducts as well). I am at my wits end on this, and I can't understand why the AHJ or the county/city inspectors sign off on this. I never see fire rated doors separating the garage from the living areas either (AHJ says any solid 1 3/8" door will suffice). More often than not, a hollow core interior door is used. In fact, I have NEVER seen a fire rated door with self closing hinges installed. I have been able to convince most if not all of my clients that they need fire separation and fire doors, but the builders just flat out don't do it during construction. Your advice sounds like a winner. I think I will make a formal written request (I have only talked to the AHJ on the phone), for a clarification, and if they still say it is O.K., I'm gonna move forward. Thanks again, Tim
Bain Posted August 15, 2008 Report Posted August 15, 2008 That wouldn't even fly here in ass backward Kentucky. Nobody installs self-closing hinges, however.
Phillip Posted August 15, 2008 Report Posted August 15, 2008 Tim is right about Birmingham. They are not putting drywall on the ceiling in the garage below living space. They say they did not adopt that code is what I was told. The last new home I did there it did not have a ceiling, the decks where installed wrong, no flashing connected to a cantilever chimney and a bay window. The builder was there and said he did not know for sure what code they where using, he thought it was the 2003 IRC and did not know what part was not adopted.
Phillip Posted August 15, 2008 Report Posted August 15, 2008 Here is some photos Image Insert: 81.32 KB Image Insert: 95.62 KB Image Insert: 83.73 KB Image Insert: 103.74 KB
Tim H Posted August 15, 2008 Report Posted August 15, 2008 Originally posted by Phillip Tim is right about Birmingham. They are not putting drywall on the ceiling in the garage below living space. They say they did not adopt that code is what I was told. The last new home I did there it did not have a ceiling, the decks where installed wrong, no flashing connected to a cantilever chimney and a bay window. The builder was there and said he did not know for sure what code they where using, he thought it was the 2003 IRC and did not know what part was not adopted. Thanks for posting that Phillip. I was going to shoot you an e-mail to see if you had run into the same thing. Tim
msteger Posted August 15, 2008 Report Posted August 15, 2008 I routinely see wooden pulldown garage ladders and call'em out every time. I do note that building codes vary, but recommend replace or retrofit to conform to modern standards for safety reasons. If I see particle board or wafer board on the walls, and can't see drywall behind it, I also call it out. Heck, I do split level homes often (or other homes w/ an integral garage) and either just see insulation or the subflooring above.
Phillip Posted August 20, 2008 Report Posted August 20, 2008 This is the garage from yesterday. Built in 2003 Image Insert: 72.53 KB
Darren Posted August 20, 2008 Report Posted August 20, 2008 Phillip, From your picture that looks like a carport; was it built as a carport and then closed in?
Phillip Posted August 21, 2008 Report Posted August 21, 2008 Originally posted by Darren Phillip, From your picture that looks like a carport; was it built as a carport and then closed in? Darren, No,It was built as a garage. This builder did all the houses he built in this subdivision this way.
Phillip Posted August 21, 2008 Report Posted August 21, 2008 Here is the shot of the house. Image Insert: 70.23 KB
msteger Posted August 21, 2008 Report Posted August 21, 2008 Apparently only a few inspectors call this out in my area, me being one of them. Astonishes me that someone (maybe a builder) puts this stuff in and it passes local code.
Tom Raymond Posted August 21, 2008 Report Posted August 21, 2008 Phillip, Was there a hose bib in the garage? Perhaps the builder covered the inside in vinyl in a misguided attempt to waterproof it for washing cars inside? Tom