Brandon Whitmore Posted February 28, 2008 Report Posted February 28, 2008 Is there anything in the code book that says you can not install a panel in a stairwell. This morning's 1940 house had the panel installed in the stairwell on an outside wall. Picture a basement stairwell, with the top 4 steps being winders (panel between winders and straight run), turning and heading to the basement. There is no landing in front of the panel. Allowed or not, I say this is a stupid installation. I thought the intent of the code for working clearances was so a person working on the panel had room to jump clear in case of emergency. I would not want to see someone fall backwards down the steps while working on the panel. The panel was updated in '00 with permits pulled, and the installation was signed off by the city.
Jim Katen Posted February 28, 2008 Report Posted February 28, 2008 Originally posted by Brandon Whitmore Is there anything in the code book that says you can not install a panel in a stairwell. This morning's 1940 house had the panel installed in the stairwell on an outside wall. Picture a basement stairwell, with the top 4 steps being winders (panel between winders and straight run), turning and heading to the basement. There is no landing in front of the panel. Allowed or not, I say this is a stupid installation. I thought the intent of the code for working clearances was so a person working on the panel had room to jump clear in case of emergency. I would not want to see someone fall backwards down the steps while working on the panel. The panel was updated in '00 with permits pulled, and the installation was signed off by the city. There's no rule against it. - Jim Katen, Oregon
Joe Tedesco Posted February 29, 2008 Report Posted February 29, 2008 Here's a new rule that was added in the 2008 NEC, that will cover this situation when this edition is adopted by the jurisdiction. "240.24(F) Not Located over Steps. Overcurrent devices shall not be located over steps of a stairway."
Brian G Posted February 29, 2008 Report Posted February 29, 2008 Originally posted by Joe Tedesco Here's a new rule that was added in the 2008 NEC, that will cover this situation when this edition is adopted by the jurisdiction. "240.24(F) Not Located over Steps. Overcurrent devices shall not be located over steps of a stairway." There's a nice addition. Brandon's right, that's a lousy place to put a panel. Brian G. Kudos to the NEC on 240.24(F) [:-angel]
John Dirks Jr Posted February 29, 2008 Report Posted February 29, 2008 Imagine working in the panel and getting a minor shock that causes you to stumble and fall down the stairs breaking your neck.
msteger Posted February 29, 2008 Report Posted February 29, 2008 Indeed a stupid location for panel location.. may follow the letter of the code, but common sense was not abided to. Doesn't the code stipulate that panelboards must be installed with specific clearances and level footing for safe access? I would think the level footing would be contradictory to staircases.
Brian G Posted March 1, 2008 Report Posted March 1, 2008 Originally posted by msteger Doesn't the code stipulate that panelboards must be installed with specific clearances and level footing for safe access? I would think the level footing would be contradictory to staircases. What I have is the 2005, and I can't find any mention of footing in it (so far). 110.26 Spaces About Electrical Equipment talks about a lot of different stuff, but no sign of "level" or "footing". It may not have previously occurred to them that some joker would mount one over stairs (or it could be somewhere else). [:-headach Brian G. A Foolish Assumption of Common Sense, Perhaps? [:-paperba
hausdok Posted March 1, 2008 Report Posted March 1, 2008 Hi, For years I've heard people talk about how this space in front of the panel is a safety issue and it's meant to provide someone a means of getting away from the panel. I'm starting to think that's just folklore; it seems more likely that electricians stuck that requirement in the code to ensure that someone working on the panel can do so easily. They might claim that it was put in there for safety but I think the bottom line is they don't want to have to be an acrobat to work on a panel, so they write a requirement into the law that mandates a space big enough for a man to stand in in front of the panel. Sure, the stairs is a dumb location, but all this talk about someone being electrocuted and then falling down the stairs and breaking his or her neck? I think some imaginations are running wild with speculation, here. OT - OF!!! M.
Jim Katen Posted March 1, 2008 Report Posted March 1, 2008 Originally posted by msteger Indeed a stupid location for panel location.. may follow the letter of the code, but common sense was not abided to. Doesn't the code stipulate that panelboards must be installed with specific clearances and level footing for safe access? I would think the level footing would be contradictory to staircases. There has never been any such rule. - Jim Katen, Oregon
Jim Katen Posted March 1, 2008 Report Posted March 1, 2008 Originally posted by Joe Tedesco Here's a new rule that was added in the 2008 NEC, that will cover this situation when this edition is adopted by the jurisdiction. "240.24(F) Not Located over Steps. Overcurrent devices shall not be located over steps of a stairway." Thanks, Joe. Oregon will be adopting the '08 NEC as of April 1.
Joe Tedesco Posted March 1, 2008 Report Posted March 1, 2008 Originally posted by Jim Katen Originally posted by Joe Tedesco Here's a new rule that was added in the 2008 NEC, that will cover this situation when this edition is adopted by the jurisdiction. "240.24(F) Not Located over Steps. Overcurrent devices shall not be located over steps of a stairway." Thanks, Joe. Oregon will be adopting the '08 NEC as of April 1. You are welcome! When push comes to shove I would use 110.3(a)( ...
Brandon Whitmore Posted March 1, 2008 Author Report Posted March 1, 2008 Thanks Guys, I went ahead and wrote it up anyway's. I just made a note of the fact that it is a safety concern to be aware of whether or not a violation.