Hey Chad,

Got the EM.

I'm not commenting on this box just yet, but it's a good reason for folks in hi rise buildings... to have a home inspections. Besides sharing electric, I've come across some amazing fire wall/penetration problems.

Never a dull moment, I'm working across the street from where the psycologist was killed on Tuesday.

Posted

Hi,

I see a number of this wrong with this panel. You ar e right about the multi wire circuit, but there is a second leg, feeding the apartment below. Anything else?

Posted
Originally posted by StevenT

Never a dull moment, I'm working across the street from where the psycologist was killed on Tuesday.

I used to live a few blocks north of there- 97th & Park. 6th floor walk up that should have been condemned long ago.

Posted

The two hots and one neutral are entering from above. The red hot leg is jumped to feed both sides of this panel, the black hot leg passes through this panel into the apartment below. They are also sharing the neutral. Besides double lugging, the main breakers are independant of each other... no breaker ties.