Neal Lewis Posted February 1, 2008 Report Posted February 1, 2008 I found some CSST buried a few inches below grade. I'm not sure what brand it was, but Gastite installation instructions says it can't be buried. Is it possible that a different brand or grade of CSST is OK buried?
inspector57 Posted February 1, 2008 Report Posted February 1, 2008 SECTION 4.9 ââ¬â UNDERGROUNDINSTALLATIONS 1. CODE REQUIREMENTS When gas piping runs are located below grade in contact with earth or other material that could corrode the piping, codes require that the gas piping shall be protected against corrosion. When piping is installed underground beneath buildings, codes require that the piping shall be encased in a conduit sealed inside of the building and vented above grade to the outside. The conduit shall be designed to withstand the superimposed loads. NO FITTINGS OR COUPLINGS ARE PERMITTED BENEATH BUILDINGS. 2. REGIONAL/MODEL CODES TracPipe PS (patented) and PS-II (patent-pending) installations conform to the underground fuel gas installation requirements of: The National Fuel Gas Code NFPA 54 The International Fuel Gas Code The Uniform Plumbing Code 2003 UPC® Trac pipe lists a specific type for underground use, but some specific requirements. http://www.omegaflex.com/trac/litlibrary/D&I_Guide.pdf
gordonwrogers Posted June 25, 2010 Report Posted June 25, 2010 Here is a CSST rated for direct burial. Check with your local code official. http://www.gastite.com/products.php?cat ... link=link3
Darren Posted June 25, 2010 Report Posted June 25, 2010 Neal; You're going to have to see if your piping is rated for underground use. However, NJ code states 'Underground piping systems shall be a minimum depth of 12 inches below grade except as provided for in section 2415.9.1 Which states...Individual lines to outside lights, grills or other appliances shall be installed a minimum of 8 inches below grade. provided that such installation is approved and installed in locations not susceptible to physical damage.
Chad Fabry Posted June 25, 2010 Report Posted June 25, 2010 Here is a CSST rated for direct burial. Check with your local code official.http://www.gastite.com/product...nk=link3 Gordon, that's polyethylene.
Recommended Posts
Create an account or sign in to comment
You need to be a member in order to leave a comment
Create an account
Sign up for a new account in our community. It's easy!
Register a new accountSign in
Already have an account? Sign in here.
Sign In Now