I found some CSST buried a few inches below grade. I'm not sure what brand it was, but Gastite installation instructions says it can't be buried. Is it possible that a different brand or grade of CSST is OK buried?
SECTION 4.9 — UNDERGROUND
INSTALLATIONS
1. CODE REQUIREMENTS
When gas piping runs are located below
grade in contact with earth or other material
that could corrode the piping, codes
require that the gas piping shall be protected
against corrosion.
When piping is installed underground
beneath buildings, codes require that the
piping shall be encased in a conduit
sealed inside of the building and vented
above grade to the outside. The conduit
shall be designed to withstand the superimposed
loads. NO FITTINGS OR COUPLINGS
ARE PERMITTED BENEATH
BUILDINGS.
2. REGIONAL/MODEL CODES
TracPipe PS (patented) and PS-II
(patent-pending) installations conform to
the underground fuel gas installation
requirements of:
The National Fuel Gas Code NFPA 54
The International Fuel Gas Code
The Uniform Plumbing Code 2003 UPC®
Trac pipe lists a specific type for underground use, but some specific requirements.
http://www.omegaflex.com/trac/litlibrary/D&I_Guide.pdf
  • 2 years later...
Neal;
You're going to have to see if your piping is rated for underground use.
However, NJ code states 'Underground piping systems shall be a minimum depth of 12 inches below grade except as provided for in section 2415.9.1
Which states...Individual lines to outside lights, grills or other appliances shall be installed a minimum of 8 inches below grade. provided that such installation is approved and installed in locations not susceptible to physical damage.