Ken Meyer Posted November 28, 2007 Report Posted November 28, 2007 Is there a minimum clearance required between a PVC exhaust flue pipe and a heat duct? Here's a zero clearance installation. Image Insert: 177.69 KB
Richard Moore Posted November 28, 2007 Report Posted November 28, 2007 Ken, I don't have the definitive answer but it doesn't seem that the circulated air, and therefore the duct, could be any hotter than the gasses being exhausted through the flue, even in a 90+ furnace. For that reason I just can't see the duct doing the plastic flue any harm, or vise versa.
Chad Fabry Posted November 28, 2007 Report Posted November 28, 2007 I don't have the definitive answer but it doesn't seem that the circulated air, and therefore the duct, could be any hotter than the gasses being exhausted through the flue, even in a 90+ furnace. I think the circulated air could very well be hotter than the exhaust temps but neither would be above the deformation point of the PVC. I don't think there's a spec and it's a self correcting problem if it does get too hot.
Eric B Posted November 28, 2007 Report Posted November 28, 2007 I've never heard of one or would expect a problem.
Brandon Chew Posted November 28, 2007 Report Posted November 28, 2007 I wouldn't expect a problem due to temperature. If they are touching, I'd be concerned that vibration could eventually wear a hole into the PVC exhaust flue. I think the risk of that happening is very low but the consequences are great enough that I would recommend they fix it so the two are not touching each other.
msteger Posted November 28, 2007 Report Posted November 28, 2007 Heck, just still an old sock between the two..
Richard Moore Posted November 29, 2007 Report Posted November 29, 2007 Originally posted by Chad Fabry I don't have the definitive answer but it doesn't seem that the circulated air, and therefore the duct, could be any hotter than the gasses being exhausted through the flue, even in a 90+ furnace. I think the circulated air could very well be hotter than the exhaust temps .... Chad, I'm trying to picture that, but keep coming up short in this old head. [:-dunce] Wouldn't that require a heat exchanger to operate at over 100% efficiency? I didn't think that was possible no matter how convoluted the exchanger. I'm seriously curious...could you (or someone else) explain?
Neal Lewis Posted November 29, 2007 Report Posted November 29, 2007 Originally posted by Chad Fabry I don't think there's a spec and it's a self correcting problem if it does get too hot. I was curious about what the self correcting problem is?
Chad Fabry Posted November 29, 2007 Report Posted November 29, 2007 If 95% of the heat is extracted from the combustion process the combustion by-product will be very cool; almost all the energy (heat content) was removed by the heat exchanger and transferred to the circulated air. Tempering the remaining heat content with unused combustion air creates a scenario where circulated air could be hotter than exhaust. The dew point of the exhaust gas is dependent on excess combustion air supplied, but it's usually around 180 degrees. So, before the exhaust leaves the furnace it's below the dew point and it just keeps getting cooler from there. When exhaust leaves an engine it's around 1400 degrees. By the time it exits the tail pipe it's usually less than 150. The self correcting bit is the flue will deform away from the ducting if it gets too hot. It won't ever get that hot though. I've done a fair amount of PVC heating and bending. At 300 degrees PVC is malleable, but not melting or sloppy.
Richard Moore Posted November 29, 2007 Report Posted November 29, 2007 Originally posted by Chad Fabry If 95% of the heat is extracted from the combustion process the combustion by-product will be very cool; almost all the energy (heat content) was removed by the heat exchanger and transferred to the circulated air. If the fan speed were slow enough I'm sure you could get air temps much higher than exhaust temps. My problem with that is that if the circulated air were hotter than the cumbustion gases at some point in the heat exchanger, then wouldn't heat want to transfer the other way...ie the circ air would actually heat the combustion gasses. If the circ blower speed was reduced, then I would expect both the circ air and combustion gasses to increase in temp, not just the circ air. I could see equalibrium being reached, but I'm still having a hard time with actually hotter. No big deal. I'm probably missing something basic here and just having a senior moment.
Brandon Chew Posted November 29, 2007 Report Posted November 29, 2007 Richard, I don't think Chad is saying the circulated air temperature would be higher than the combustion gases where the two are passing each other inside the heat exchanger. He's saying that on a high efficiency furnace the exhaust gasses will quickly cool to a temperature below the circulated air temp after this point. Brandon
Richard Moore Posted November 29, 2007 Report Posted November 29, 2007 Yep, I think that's my problem. I've been assuming we were talking about the hottest point of the gases where the plastic flue is first allowed to be used, right at the furnace connection, and I believe Chad was talking about somewhere cooler, further downstream (actually up of course for drainage).
Chad Fabry Posted November 29, 2007 Report Posted November 29, 2007 Hi Richard, Sorry, I haven't been focused lately and I'm missing a communication gene. What Brandon said and you surmised.