ctgo4it Posted June 22, 2007 Report Posted June 22, 2007 I saw this on a main disconnect this week. i don't recall ever seeing anything like this. Anyone ever see this, or know why it's there? Thank you Image Insert: 34.36 KB
charlie Posted June 22, 2007 Report Posted June 22, 2007 Yes it is supposed to be there to hold the breaker in when it is being used as a main disconnect
Jim Katen Posted June 22, 2007 Report Posted June 22, 2007 Originally posted by ctgo4it I saw this on a main disconnect this week. i don't recall ever seeing anything like this. Anyone ever see this, or know why it's there? Thank you As Charlie said, it's supposed to be there. Whenever you have a backfed breaker -- when the power enters through the breaker's terminals and then goes to the busbar -- the breaker is supposed to be secured to the panel so that you can't just pull it out. If you could, it'd be dangerous to have a live breaker flopping around on the end of some wires. The screw you saw is one way to do it. Another was is to use a proprietary clip that the manufacturer provides for just this purpose. These are sometimes hard to see. Here's a picture of one of these hard-to-see clips. - Jim Katen, Oregon Image Insert: 74.08 KB
ctgo4it Posted July 1, 2007 Author Report Posted July 1, 2007 now that you mention it, I've started checking for, and noticing the clips. Thanks