Brandon Whitmore Posted May 11, 2007 Report Posted May 11, 2007 Just did an inspection for a one year warranty. Typical meter main installation with a distribution panel in the garage. The neutral and ground bus bars were not bonded together, but the neutral wires running off the AFCI breakers were attached to the ground bus bar. This seems like an improper installation to me, but was wired by an electrician and signed off by the city inspector. -- can anyone tell me whether or not this is allowed? Thanks
Jim Katen Posted May 11, 2007 Report Posted May 11, 2007 Originally posted by Brandon Whitmore Just did an inspection for a one year warranty. Typical meter main installation with a distribution panel in the garage. The neutral and ground bus bars were not bonded together, but the neutral wires running off the AFCI breakers were attached to the ground bus bar. This seems like an improper installation to me, but was wired by an electrician and signed off by the city inspector. -- can anyone tell me whether or not this is allowed? Thanks If you're talking about the little coiled white wire that comes out of the AFCI device, you're correct. It's supposed to be connected to the neutral bar, not the grounding bar. The printed instructions are very clear on the matter. - Jim Katen, Oregon
Brandon Whitmore Posted May 12, 2007 Author Report Posted May 12, 2007 Jim, Once again, Thanks (yes it was the little coiled white wire)