Recommended Posts

Posted

Wire size used for A/C condensor unit is 12/2, common yellow Romex.

Rating on unit says minimum circuit ampacity

is 20.2 amps.

Breaker was 30 amp, which is within max breaker size on unit.

Is 12 gauge enough?

Posted
Wire size used for A/C condensor unit is 12/2, common yellow Romex.

Rating on unit says minimum circuit ampacity

is 20.2 amps.

Breaker was 30 amp, which is within max breaker size on unit.

Is 12 gauge enough?

Yes, #12 is fine, it's ampacity is 25 amps.

- Jim Katen, Oregon

Posted
Originally posted by Chad Fabry

Mr. Katen, it has taken 5 years but you have let me down.

Hmm. How so?

Surely you're not confusing the ampacity of a wire with its overcurrent protection rating.

- Jim Katen, Oregon

Posted

Thanks Chad, now I'll remember. It's one of those words where I have a mental block in regards to the correct spelling.

The it's word is misused a-lot. Five years is a pretty good track record.

Posted

Jim, Chad started this so don't take it out on me.

"Common yellow Romex"??

And, Yes 12 gauge is enough for low flying ducks and bunnies.

Seriously - it was a good question.