Jump to content

Recommended Posts

Posted

Brian...because you asked, and I love a challenge. [;)]

First, this is from Eaton's (Cutler-Hammer) tech library on CH load-centers.

Download Attachment: icon_photo.gif ScreenHunter_3.jpg

54.19 KB

You will notice that 40 circuits is not a listed option.

And then this, to prove they exist.

http://doityourself.com/store/6065577.htm#

I'm not saying the ratsnest panel is OK...as you pointed out, the label will tell. And...it does seem that some manufacturers do have 40 circuit limits for some panels. I'd just never heard of a hard and fast 200/40 225/42 rule.

Posted

Well as I live and breath; now I've seen one. You've just gotta love the 200 amp 42 circuit panel as a DYI item, don't you? [:-dunce]

I sort of wonder about Cutler-Hammer though. They have that other double-tap breaker on the market, but unlike the Square D the lug looks totally generic...like they just grabbed one out of stock and went for it.

Good find Richard. Exception duely noted, and I stand corrected. [:-paperba

Brian G.

Me and My Big Mouth [:-bigmout

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
×
×
  • Create New...