SNations Posted December 22, 2021 Report Posted December 22, 2021 Chicago house built 2005. The panel clearly doesn't allow any tandem breakers, right? Based on the schematic and the catalog number. So if there's a tandem breaker or two, and they're marked "CTL", would somebody have had to physically alter the breaker in order to make it fit?
Jim Katen Posted January 9, 2022 Report Posted January 9, 2022 Yes, they would. I pop these out and take a picture of the shattered plastic on the back. (I know, I know, gosh whiz, inspectors aren't supposed to do that. I say fuck it.)
Les Posted January 10, 2022 Report Posted January 10, 2022 On 1/9/2022 at 2:39 AM, Jim Katen said: Yes, they would. I pop these out and take a picture of the shattered plastic on the back. (I know, I know, gosh whiz, inspectors aren't supposed to do that. I say fuck it.) I note you had another birthday recently. Age has its privilege.😄😄
Jim Katen Posted January 11, 2022 Report Posted January 11, 2022 Yes, it seems that I've taken a turn onto the curmudgeon highway. 1
Scott Malkinson Posted January 20, 2022 Report Posted January 20, 2022 It's a SqD Homeline breaker in a Siemens panel (not listed to be in the panel in the first place). The CTL marking has no relevance.
Jim Katen Posted January 24, 2022 Report Posted January 24, 2022 On 1/20/2022 at 11:00 AM, Scott Malkinson said: It's a SqD Homeline breaker in a Siemens panel (not listed to be in the panel in the first place). The CTL marking has no relevance. It's relevant because it means that the breaker had to be damaged in order to fit into the panel. Simply installing the wrong brand breaker in a panel is a very minor issue that's unlikely to have any impact on anything in the real world. Physically breaking the case of a breaker is a larger concern.
Scott Malkinson Posted January 24, 2022 Report Posted January 24, 2022 Doesn't the mismatched panel/breaker combination issue render the CTL issue a moot point? Are there differing degrees of wrong?
CNewhouse Posted January 25, 2022 Report Posted January 25, 2022 8 hours ago, Scott Malkinson said: Are there differing degrees of wrong? I would say there undoubtedly are. A category I furnace with a B vent sloped at 1/8" per foot is wrong. A category I furnace with a PVC exhaust vent is very wrong and dangerous. Silly example, yes, but there is absolutely a spectrum of concern when it comes to defects in the various systems. To assign every issue equal significance would be a disservice to the client. Many know little about homes and how they work.
Jim Katen Posted January 26, 2022 Report Posted January 26, 2022 On 1/24/2022 at 11:25 AM, Scott Malkinson said: Doesn't the mismatched panel/breaker combination issue render the CTL issue a moot point? Are there differing degrees of wrong? I think it's the other way around. A shattered breaker renders the mismatched brand a moot point. A shattered breaker is a whole 'nuther level of wrong.
ejager Posted March 20, 2022 Report Posted March 20, 2022 (edited) Home inspection as a risk assessment... there is no absolute right or wrong. We need only explain the risk levels if not self evident (and according to my insurance company - its never evident so when I point out a pipe leak, I have to say " Water leaks can damage contents, materials, structure and may cause mould. Possible hidden damage". And each client has their own level of risk tolerance for any particular problem - or for each side of the triangle. Some are good with vermiculite - some have personal experience with a stove missing an anti-tip bracket, or leaking fridge that makes them averse to appliance concerns. Some have the money to deal with the consequences, some have the skills to lower the risks... I never know and it doesn't matter. Edited March 20, 2022 by ejager