Jerry Simon Posted February 11, 2021 Report Share Posted February 11, 2021 (edited) Entire panel is energized. What's going on with the *off* main breaker leg? (Second from left; kinda hard to see). Just one leg in use on each side? Couldn't flip breaker legs to check; house occupied. Edited February 11, 2021 by Jerry Simon Link to comment Share on other sites More sharing options...
Jim Katen Posted February 12, 2021 Report Share Posted February 12, 2021 Looks like somebody smacked the handle tie, breaking off the ends of all 4 handles. The left pole will only provide half the intended power because one of its breakers is switched off. If that's a 200-amp panel, it's unlikely to be an issue because few homes will actually draw 100 amps from one pole at any given time. And if the house tried to draw much more, the other breaker will just trip. Of course, the entire main breaker should be replaced. Link to comment Share on other sites More sharing options...
hausdok Posted February 12, 2021 Report Share Posted February 12, 2021 Yeah, all four are broke; it's just that the second from the left is more broke than the other three. Ha ha. Link to comment Share on other sites More sharing options...
hausdok Posted February 14, 2021 Report Share Posted February 14, 2021 About twenty or so years ago, there was this forensic engineering firm in North Carolina that reported issued with 200 amp Siemens load centers. They would get hot and eventually melt down and burn through the back of the panel. At the time, they'd investigated about seven cases and were looking for more. I bet that Google could find that report for you. ONE TEAM - ONE FIGHT!!! Mike Link to comment Share on other sites More sharing options...
Recommended Posts
Create an account or sign in to comment
You need to be a member in order to leave a comment
Create an account
Sign up for a new account in our community. It's easy!
Register a new accountSign in
Already have an account? Sign in here.
Sign In Now