If this is a service entrance conductor that's carrying the entire load of the service and if there are no derating issues at play, then you only need to size the wire at 83% of the load. In effect, a 100-amp service only needs to have 83-amp service entrance wires. That makes #2 AL THW a perfectly valid choice. 

  • Like 1
Link to comment
Share on other sites

Depends on the edition of the NEC. That table was removed in the 2014 & 2017 NEC editions and replaced with the 83% rule. Then the 2020 edition brought it back, but it's now Table 310.12 and it carries the caveat that it can only be used when there are no adjustment or correction factors required. It's exactly the same as the document that I attached. 