Marc Posted June 23, 2019 Report Posted June 23, 2019 I've got this water heater installed in a sheet metal lean-to on the side of today's house. The gas appliance connector starts just inside the crawl, exits the crawl in plain view, then goes through an opening into the lean-to. Everything on this new heater install looks DIY. Is this appliance connector ok?
Bill Kibbel Posted June 23, 2019 Report Posted June 23, 2019 I would say no. A connector shouldn't pass through a wall, partition or housing.
Jim Katen Posted June 23, 2019 Report Posted June 23, 2019 And the appliance shutoff valve has to be upstream of the connector AND in the same room as the appliance. . .