Mark P Posted August 25, 2018 Report Posted August 25, 2018 Hi, It has been a longtime since I've posted... Hope everyone is well. Here is my question. There is a main panel with a 30 amp circuit running to a subpanel; 30 amp breaker in main panel and #10 running between the 2 panels. In the subpanel there is a 100 amp main disconnect. So the #10 runs from a 30 amp breaker in the main panel to a 100 amp breaker in the subpanel. Is this allowed. It seems the wire would be protected by the 30 amps breaker and the 100 amp breaker is irrelevant. I'm sure I'm over thinking this and at onetime I new the answer. Thanks for the help. Mark P.
Chad Fabry Posted August 26, 2018 Report Posted August 26, 2018 It's fine. The 100 amp breaker is just a switch. Nice to hear from you. Stop by and visit more.
John Kogel Posted August 26, 2018 Report Posted August 26, 2018 (edited) Right, it is good practice to write '30 amps Max' somewhere on the subpanel front, but it is not required by the NEC, AFAIK. Edited August 26, 2018 by John Kogel
Mark P Posted August 26, 2018 Author Report Posted August 26, 2018 Thanks guys, I've been back lurking for awhile. I'll make an effort of participate more often.
Recommended Posts
Create an account or sign in to comment
You need to be a member in order to leave a comment
Create an account
Sign up for a new account in our community. It's easy!
Register a new accountSign in
Already have an account? Sign in here.
Sign In Now