Aaarrrggh! I know that's in the IRC somewhere, I saw it last week in class. I just dug back and forth in the book and couldn't find it though. Damn big-a** book...

I'll try again in a little while.

Brian G.

Frustrated Flipper [:-grumpy]

Posted

Around here, wiring is permitted to pass through return air cavities.

E3804.7 Air handling-stud cavity and joist spaces. Where wiring methods having a nonmetallic covering pass through stud cavities and joist spaces used for air handling, such wiring shall pass through such spaces perpendicular to the long dimension of the spaces.

Posted

Brain cramp, disregard! I found what I was thinking of, but it's about gas piping (G2415.1), not wiring or refrigeration lines. [:-paperba

Brian G.

Still Code-fused From 3 Days of Heavy Exposure [:-boggled

Posted

In the 2003 IMC

Section 602.2.1 Materials exposed within plenums.

There is a list of items that cannot be installed in plenums (please note, a plenum is not a duct). However, under exceptions;

3) This section shall not apply to materials exposed within plenums in one- and two-family dwellings.

The only area (that I could find) that mentions materials in ducts is;

601.3 Contamination prevention.

Exhaust ducts under positive pressure, chimnys and vents shall not extend into or pass through ducts or plenums.

Here's a question:

Does anyone know the difference between a flexible air duct & a flexible air connector?

Darren

www.aboutthehouseinspections.com

Posted

Don't forget that the codes are not the answer for everything. Codes are the minimal standard, and not always the best standard.

A return air chase should be clean and sealed, but it provides an easy access to the attic for anyone looking to install something. It is the favorite hiding place for alarm horns and the like.

As for refrigerant lines in a return chase just think about the problems that could arise. The first that jumps out is a condensation problem and all of the water that could collect and start a breeding ground for mold. So the contractor insulates the lines with neoprene foam sleeves. Now we have introduced foam that produces toxic gases when it burns, into the return air.

Posted
Originally posted by BlackJack

Download Attachment: icon_photo.gif Slide36.JPG

92.61 KB

Looking up to the 2nd floor. Horiz. Gas Furnace in 2nd floor closet.

That return air chase doesn't appear to be sealed. It looks like return air is coming from through wall cavities and all kinds of places that might deliver who knows what. There are more problems than the gas piping and wiring.

Posted

I had the sewer vent in the narrative of the report, just didn't get it in the picture.

The air return to the furnace has only the space between the floor joists, and who knows if the floor joist area is sealed.