Catmando Posted August 8, 2017 Report Share Posted August 8, 2017 I saw this today. Haven't seen anything exactly like it. It's a General Electric panel ( with some Square D breakers ). The service line has one leg attached to a 70 amp breaker, and another leg attached to a parallel bus. The 70 amp breaker has two leads leading to lower areas of the bus. I want to call this a 70 amp service with a split bus panel. I don't understand how the 70 amp breaker would act as a main shutoff. Link to comment Share on other sites More sharing options...
Jerry Simon Posted August 8, 2017 Report Share Posted August 8, 2017 (edited) It is a split bus panel. A split bus panel does not have a main disconnect. The service capacity is determined by the service entrance cable size and/or the rating of the main panelboard, not the 70-amp breaker. Edited August 8, 2017 by Jerry Simon Link to comment Share on other sites More sharing options...
Bill Kibbel Posted August 9, 2017 Report Share Posted August 9, 2017 7 hours ago, Catmando said: The service line has one leg attached to a 70 amp breaker, and another leg attached to a parallel bus. Both service legs are attached to buses. The 70 amp breaker supplies a separate pair of buses below. Don't need a single main breaker, but there are supposed to be no more than 6 breakers/disconnects in the top part to shut off everything. The one pictured has 7. Link to comment Share on other sites More sharing options...
Jim Katen Posted August 9, 2017 Report Share Posted August 9, 2017 . . . and some split bus panels don't allow single pole breakers or tandem breakers in the upper section. See the schematic on the panel; it reveals all. Link to comment Share on other sites More sharing options...
Recommended Posts
Create an account or sign in to comment
You need to be a member in order to leave a comment
Create an account
Sign up for a new account in our community. It's easy!
Register a new accountSign in
Already have an account? Sign in here.
Sign In Now