greyboy39 Posted May 17, 2017 Report Posted May 17, 2017 Saw a double tapped ground lug today, ground feeder to 60 amp garage subpanel. Is this condition ever allowed. The house is owned by an electrician and this is the only reason Im questioning if there are allowances for this condition.
Chad Fabry Posted May 17, 2017 Report Posted May 17, 2017 If that panel is the service equipment and the terminal is rated for two wires (it's probably not) then it's OK.
greyboy39 Posted May 17, 2017 Author Report Posted May 17, 2017 It is the main panel. Is there anyway to tell if the terminal is rated for two wires? Ive read that snowman shaped terminals/lugs are designated for two wire installations.
Jim Katen Posted May 18, 2017 Report Posted May 18, 2017 42 minutes ago, greyboy39 said: It is the main panel. Is there anyway to tell if the terminal is rated for two wires? Ive read that snowman shaped terminals/lugs are designated for two wire installations. If it's listed for two wires, that information will be stamped on the lug or on the schematic.
adarty Posted May 21, 2017 Report Posted May 21, 2017 As Jim Katen mentioned, the lug will bear a stamp giving number of conductors and size of acceptable conductors. Aluminum SE and a copper conductor under the same screw at that lug? I thinks that is just asking for trouble...