A flooring installer makes these good looking air supply grilles that match the material he installs.
Does anyone here think that the design restricts air flow enough to affect equipment operation or performance?
Which leads me to a further question. Are air supply grilles among pieces of equipment that are listed and tested for the use?
45.25 KB
52.48 KB
Link to comment
Share on other sites
I agree with Kurt. The component in a distribution duct that most affects the resultant air flow is the register. Small changes in register design can make big changes in air-flow rates.
I would absolutely be writing that one up:
Custom made ceiling/floor registers are installed. These registers ruin the results of any duct system calculations done to match air flow rates to heat loads in individual rooms. You should ask your AC contractor to replace these registers. Depending on the condition of the remainder of the duct system, your AC contractor might recommend the additional step of repeating manual J and manual D calculations to confirm proper duct system design.
Link to comment
Or....
"These custom registers drastically reduce air flow; the room may not heat or cool adequately. If that's the case, replace these registers with conventional models." Take a picture and have an arrow pointing at a register.
Please don't write stuff like you wrote. Next thing, you'll be using words like "imbricated". You're one of my last hopes in this gig for a shot at making things move forward. Everyone thinks the opposite of the way the world's moved, and they're proud of it. You seem to pay attention. Write like it. Please. With sprinkles on top.
In my entire career I've seen a Manual J about twice. Maybe 3 times. No one's going to do a Manual J for a home inspection.
Put your hand over the register; if you can't tell if the air flow is sufficient, keep practicing until you can. When it's not, say so. It's just a house. It's not complicated.
Link to comment
Thanks for the replies, guys.
So, to my second question. I suppose these tech manuals you reference will speak of register/grille flow rates or opening specs, or maybe reference again some standard re the product? Surely a manufacturer install spec would not go that far out a limb? I have never noticed anything stamped, such as you see on foundation vents to spec net free area.
Link to comment
AFAIK, manufacturers attach specified 'air resistance' values to each of their register products. Now, I haven't completed a computer-based Manual D or J calc myself yet (I'm still stuck on cardboard calculators), but I suspect there is data entered into them that reflects the resistance properties of the register.
Kurt is correct...again, on all counts. I just love it when I find there is still more to learn.
Link to comment