kurt Posted April 15, 2015 Report Share Posted April 15, 2015 Fiber cement architectural panels nailed to framing, sheathing is Denshield gyp board (near as I can tell from a few peeks in the basement), my best guess (by peeking corners and seams) of the WRB is plain old Tyvek with some roofing felt in a few locations. Z channel between horizontal joints. Nails are pulling through in a few locations, no apparent good drainage plane, looks like some of the seams are lifting a bit. 2 year old house. Opinions welcome.... Click to Enlarge 14.67 KB Click to Enlarge 17.32 KB Click to Enlarge 23.99 KB Click to Enlarge 19.35 KB Click to Enlarge 18.74 KB Click to Enlarge 15.52 KB Click to Enlarge 23.99 KB Link to comment Share on other sites More sharing options...
palmettoinspect Posted April 15, 2015 Report Share Posted April 15, 2015 Never seen the cement fiber panels without the "H" strips or battens. That stuff moves a lot around here depending on its exposure. It's not really uncommon to see cracks at the face nails. Were the nails overdriven, or were the panels installed too tight and now they're popping outward? How straight were the walls? Worst stuff I see is almost always the framers fault! At least they didn't caulk the siding to the flashing! Link to comment Share on other sites More sharing options...
Marc Posted April 15, 2015 Report Share Posted April 15, 2015 Kiel has got me wondering how cases of overdriven fasteners are distinguished from cases of fasteners that have pulled through. Marc Link to comment Share on other sites More sharing options...
kurt Posted April 15, 2015 Author Report Share Posted April 15, 2015 Walls were pretty PLS. The rest of the house was actually decent. I'd say the nails were pulling through; they weren't overdriven. The panels were pushing out where the nails were pulled through. My take is a lack of adequate drainage behind the panels. Not even grooved tyvek. No air gap whatsoever....panels tighty tight to the WRB. There is a slight lifting/swelling at the vertical seams. Water isn't getting out. My question is....is water getting in? No way to tell without taking it all apart...which is what I'm going to say in the report. Click to Enlarge 22.96 KB Link to comment Share on other sites More sharing options...
mjr6550 Posted April 15, 2015 Report Share Posted April 15, 2015 If I saw that I would be tempted to ask when they are going to install the siding. That stuff looks like crap. Link to comment Share on other sites More sharing options...
Mike Lamb Posted April 15, 2015 Report Share Posted April 15, 2015 I would go to Hardie-board for guidance if you haven't. Those may be Z-flashings between the boards and no issue unless you see some interior moisture problems. I don't know what Hardie recommends for popped nails. Link to comment Share on other sites More sharing options...
Jim Katen Posted April 15, 2015 Report Share Posted April 15, 2015 In your picture, it looks like there are no fasteners at all in the field of each panel, only around the perimeter. If so, the installation is in big trouble. Link to comment Share on other sites More sharing options...
Marc Posted April 15, 2015 Report Share Posted April 15, 2015 It looks like cut rate construction, not unlike what I've seen around here. My experience with that construction is that the exterior framing is often very uneven, especially at floor diaphragms. Bending FC panels around protruding rim joists or subflooring and such then nailing them under tension is going to later result in some nails that look like they've pulled through because the panels have sprung out around the nails, relieving the tension. Just my two-bits. Marc Link to comment Share on other sites More sharing options...
kurt Posted April 15, 2015 Author Report Share Posted April 15, 2015 In your picture, it looks like there are no fasteners at all in the field of each panel, only around the perimeter. If so, the installation is in big trouble. I hadn't weighted that as much as I should be. I think you're right. Link to comment Share on other sites More sharing options...
kurt Posted April 15, 2015 Author Report Share Posted April 15, 2015 Bending FC panels around protruding rim joists or subflooring and such then nailing them under tension is going to later result in some nails that look like they've pulled through because the panels have sprung out around the nails, relieving the tension. Just my two-bits. Marc You know, that could be. I think that might be going on in some areas. Link to comment Share on other sites More sharing options...
Rob Amaral Posted April 15, 2015 Report Share Posted April 15, 2015 Perhaps an IR thermography survey should be done as part of this correction/evaluation Kurt. I've been recommending such for similar issues and these 'where are the ice-dam leak area' issues.. Link to comment Share on other sites More sharing options...
kurt Posted April 15, 2015 Author Report Share Posted April 15, 2015 I scanned it. Nothing definitive other than a couple spots that one might barely construe as anomalies, and which would require excavation to verify. So far, for me anyway, IR just points at where I should dig. I'm thinking the lack of fasteners and zero air space in the "drainage plane" are the problem. If they refasten/nail more fasteners, then they're perforating the WRB. My view of this is it's looking like trouble. Link to comment Share on other sites More sharing options...
kurt Posted April 15, 2015 Author Report Share Posted April 15, 2015 I would go to Hardie-board for guidance if you haven't. Those may be Z-flashings between the boards and no issue unless you see some interior moisture problems. I don't know what Hardie recommends for popped nails. I don't know if it's Hardi material, but it doesn't look like any of the Hardi Panel materials I've seen. Cut and pasted from Hardie....most current.... "Rainscreen application for panels - Effective September 1, 2013, James Hardie will require that HardiePanel Vertical Siding is attached over a minimum 3/8" furring to create an air space behind the panel." That confirms my largest suspicion. No air, it can't work right. Link to comment Share on other sites More sharing options...
Rob Amaral Posted April 16, 2015 Report Share Posted April 16, 2015 Sounds like it needs to be removed... 'shoddy installation'.. Link to comment Share on other sites More sharing options...