Is there anything wrong with mixing SEC conductors metals?

Click to Enlarge
tn_2014913143610_061elec.jpg

30.77 KB

Look at the corrosion on the lugs and you have your answer and your answer is yes, there is a problem with mixing materials.

Posted

The truth of the matter is there is NO problem with using copper for one leg and aluminum for another leg.

The NEC is quiet on that. As long as each leg is sized properly why would there be a problem ? Each leg is completely independent of each other.

Posted

Both legs look like copper to me. Am I not seeing it correctly?

Copper SEC into aluminum lugs. In that case, would paste make any difference?

My guess is they are both copper. The one is corroded/oxidized.

I am willing to bet that they are not aluminum lugs.

My reply was a general reply that one can use aluminum and / or aluminum as a feed/ feeder

Posted

As long as the lugs are listed for use with either aluminum or copper, it's not a problem.

Then how do you explain the corrosion on the lugs?

Corrosion can be caused by all sorts of things other than incompatible metals. We all see it all the time. It could be that there were originally two aluminum wires, and one of them corroded and was replaced by copper.

  • 2 weeks later...
Posted

The conductors appear to be the same size. This would be an issue if one is AL. (lower ampacity rating)

Your eye might be better than mine, but there might also be some optical illusion because of the different colors. When I hold up a caliper to my screen, the two conductors seem to be nearly identical in diameter. Since compact stranded aluminum wire is typically smaller in diameter than copper wire of the same gauge, I suspect that the aluminum is at least one gauge larger than the copper. It's really hard to tell.

Posted

Foundation crack at the service entry ell; finished basement covered it up. Sucker probably leaked for a decade, then someone finally patched it with epoxy injection.

The equipment was shot. That white powder thing is wild; the disconnect had pretty much gone to borax; I don't know how it was conducting electricity.

Posted

What about this? The whole mess was turning into white powder.

Click to Enlarge
tn_2014926235030_DSCN5889.jpg

48.49 KB

When I see that I look for water stains on the service entrance conductors entering the top of the panel. Water often enters the meter socket and flows into the panel.

Click to Enlarge
tn_201492822732_P9238794%20(512x384).jpg

35.81 KB

Click to Enlarge
tn_201492822825_P9238797%20(512x384).jpg

31.28 KB

Posted

Aluminum wires don't like to get wet. I was working in my shop one day when I lost power on one leg of the 240-volt feeder. The pictures show what I found when I dug it up.

Maybe because its anodic index is so high. Remember galvanic action between dissimilar metals? 2000 series wrought aluminum is -0.75 whereas copper is only -0.35.

Marc

Posted

Aluminum wires don't like to get wet. I was working in my shop one day when I lost power on one leg of the 240-volt feeder. The pictures show what I found when I dug it up.

Maybe because its anodic index is so high. Remember galvanic action between dissimilar metals? 2000 series wrought aluminum is -0.75 whereas copper is only -0.35.

Marc

That could well be it, but I don't know what the cathode would be in that trench. There aren't any copper deposits here.