Main panel is 300 feet up the road. 3 wire going down to house. 2005 build. Should be 4 wire, right?

Click to Enlarge
tn_2014426174410_Beck42614%20140%20(Small).jpg

44.35 KB

Sub at house appears to have floating neutrals with one tiny 12gage going to the equipment grounds.

Click to Enlarge
tn_2014426174725_Beck42614%20090%20(Small).jpg

46.17 KB

Click to Enlarge
tn_201442617488_Up%20r.jpg

232.1 KB

Would that 3 wire feed be OK if the neutrals were properly bonded to the panel?

Click to Enlarge
tn_2014426175121_top%20r.jpg

107.76 KB

Click to Enlarge
tn_2014426175218_Lo%20r.jpg

308.53 KB

Click to Enlarge
tn_2014426175310_Up%20L.jpg

213.54 KB

Click to Enlarge
tn_2014426175354_Lo%20L.jpg

246.54 KB

Posted

Perhaps those pics were too close.

Click to Enlarge
tn_2014426204336_Beck42614%20086%20(Small).jpg

51.84 KB

Click to Enlarge
tn_2014426204359_Beck42614%20085%20(Small).jpg

44.22 KB

Click to Enlarge
tn_2014426204426_Beck42614%20084%20(Small).jpg

54.81 KB

Click to Enlarge
tn_2014426204518_Beck42614%20089%20(Small).jpg

53.71 KB

Click to Enlarge
tn_2014426204543_Beck42614%20088%20(Small).jpg

46.97 KB

Click to Enlarge
tn_201442620465_Beck42614%20087%20(Small).jpg

52.78 KB

Posted

What Jim said. Neutral must not be bonded in that sub panel, only up at the main panel.

That one neutral on the grounding bus is in the main panel, right? It wouldn't work in the subpanel with a 3-wire feed.

They forgot the cable clamp, too. Amateurs. [:-party]

Posted

WHOA there folks - before everyone gets their panties in a wad, and before we create a mob to hang that electrical inspector, lets get ALL the facts !!!

It could very well have been perfectly legal !

We NEED to know if there are any metallic paths between the 2 panels ?

I ask because in the 2002 & the 2005 it was allowed to run the 3 wire feeder if there was not metallic paths ties that tie the 2 structures together, and there in no GFCI protection of equipment on the supply side of the feeder.

Posted

There's no visible sign of a grounding conductor in the subpanel, certainly none of sufficient gauge for the size of the feeder.

The inspector's tag doesn't mean he allowed all that mess. I think 'Temp' means he approved a temporary installation, that has had additions over the years most likely. Certainly a circuit or two has been added by an amateur and there is plenty not right with that installation. IMO.

Posted

WHOA there folks - before everyone gets their panties in a wad, and before we create a mob to hang that electrical inspector, lets get ALL the facts !!!

It could very well have been perfectly legal !

We NEED to know if there are any metallic paths between the 2 panels ?

I ask because in the 2002 & the 2005 it was allowed to run the 3 wire feeder if there was not metallic paths ties that tie the 2 structures together, and there in no GFCI protection of equipment on the supply side of the feeder.

Agreed.