Marc Posted March 8, 2014 Report Posted March 8, 2014 Click to Enlarge 47.25 KB I've seen this many times but I don't recall seeing it used outdoors. Can't find it in the 08' NEC. It's not the usual liquid-tight. My question is what NEC type is it and is it allowed to be exposed to the elements. Thanks. Marc
mjr6550 Posted March 8, 2014 Report Posted March 8, 2014 I forget the name for it. I think electricians refer to it as Smurf tubing or something similar.
Chad Fabry Posted March 8, 2014 Report Posted March 8, 2014 ENT- electrical non-metallic tubing. It is not liquid tight. 362.12 Uses Not Permitted. ENT shall not be used in the following: (1) In any hazardous (classified) location, except as permitted by other articles in this Code (2) For the support of luminaires and other equipment (3) Where subject to ambient temperatures in excess of 50?C (122?F) unless listed otherwise (4) For conductors or cables operating at a temperature higher than the ENT listed temperature rating Exception to (4): Conductors or cables rated at a temperature higher than the ENT listed temperature rating shall be permitted to be installed in ENT, provided they are not operated at a temperature higher than the ENT listed temperature rating. (5) For direct earth burial (6) Where the voltage is over 600 volts (7) In exposed locations, except as permitted by 362.10(1), 362.10(5), and 362.10(7) ( In theaters and similar locations, except as provided in 518.4 and 520.5 (9) Where exposed to the direct rays of the sun, unless identified as sunlight resistant (10) Where subject to physical damage
patt Posted March 8, 2014 Report Posted March 8, 2014 One brand of many, this brand is not UV resistant http://www.carlonsales.com/flexplusblueentnmt.php Brochure Download Attachment: FAQ-ENT.pdf 34.98 KB