Marc - I think you missed the part where he said "detached building."

Every building with a panel requires a disconnect at that building in accordance with 225.32. The rule essentially mirrors the rule for service conductors.

Posted

Didn't miss anything Douglas. Seems I've had it wrong for decades. Didn't know a local main disc was required on a subpanel that served a detached structure. No muni inspector has ever written me up for it.

Marc

Posted

The disconnect may be as simple as a single or double pole toggle switch, a pullout disconnect, 6 throws or less or a main breaker. The NEC has required this for as long as I can remember.

Why a labor organization would have an exception to a code escapes me.

Posted

The disconnect may be as simple as a single or double pole toggle switch, a pullout disconnect, 6 throws or less or a main breaker. The NEC has required this for as long as I can remember.

Why a labor organization would have an exception to a code escapes me.

Jim - one of the limitations of the internet is that you can't always see when Kurt has his tongue firmly implanted in his cheek. I think this is one of them.

Posted

Yeah, I was kinda making a joke to Jerry.

Although, we do operate in a code soup here. Every municipality has it's own adoptions, and the CoCBD municipal building code is a swamp. I dream of the simplicity of the IRC.