BYC Posted August 22, 2013 Report Posted August 22, 2013 Hey everyone. I live in a top floor apartment in Los Angeles County, California where the condensate drain is routed to the bathroom sink and taps into the drain before the trap. This is a violation of the IRC. Can anyone help me understand why this would have passed inspection and what the reasoning is for this restriction within the IRC. Also, are there potential hazards (fumes, others, etc...) to the inhabitants of the apartment? Any help would be appreciated. Thanks.
Marc Posted August 22, 2013 Report Posted August 22, 2013 ...where the condensate drain is routed to the bathroom sink and taps into the drain before the trap. By 'before the trap', do you mean it's between the basin and the trap? Marc
BYC Posted August 22, 2013 Report Posted August 22, 2013 Correct. The connection occurs between the basin and the trap.
SNations Posted August 22, 2013 Report Posted August 22, 2013 Who says it's a violation of the IRC? Can you quote a section or reference a section number? Your local jurisdiction may not allow it, but that's for them to explain. I would point to section 1411.3 to show that it's not a violation.
BYC Posted August 22, 2013 Report Posted August 22, 2013 P2706.1 General. Every waste receptor shall be of an approved type. Plumbing fixtures or other receptors receiving the discharge of indirect waste pipes shall be shaped and have the capacities to prevent splashing or flooding and shall be readily accessible for inspection and cleaning. Waste receptors and standpipes shall be trapped and vented and shall connect to the building drainage system. A removable strainer or basket shall cover the waste outlet of waste receptors. Waste receptors shall be installed in ventilated spaces. Waste receptors shall not be installed in bathrooms or in any inaccessible or unventilated space such as a closet. Ready access shall be provided to waste receptors. P2706.3 Prohibited Waste receptors. Plumbing fixtures that are used for domestic or culinary purposes shall not be used to receive the discharge of indirect waste piping. Exceptions: 1. A kitchen sink trap is acceptable for use as a receptor for a dishwasher. 2. A laundry tray is acceptable for use as a receptor for a clothes washing machine.
Marc Posted August 22, 2013 Author Report Posted August 22, 2013 Perhaps the code inspector didn't know it was a violation, didn't notice it or simply didn't care. I don't know how it could be a hazard. Condensate lines plug sometimes but those are 3/4 inch AC contractor-installed lines not 1 1/4 or 1 1/2 plumber-installed drains. Marc
Nolan Kienitz Posted August 22, 2013 Report Posted August 22, 2013 All primary condensate drain lines for HVAC systems (usually located in attics in Texas) route to a bathroom sink drain (first or second floor ... depends on house style) and is always "above" the P-Trap. Biggest hiccup I see is that the HVAC installer will often use a thick radiator type hose from the PVC in the wall penetration to the drain line connection and they end up "crimping" the hose which block the condensate flow. Click to Enlarge 24.47 KB
SNations Posted August 22, 2013 Report Posted August 22, 2013 P2706.1 General. Every waste receptor shall be of an approved type. Plumbing fixtures or other receptors receiving the discharge of indirect waste pipes shall be shaped and have the capacities to prevent splashing or flooding and shall be readily accessible for inspection and cleaning. Waste receptors and standpipes shall be trapped and vented and shall connect to the building drainage system. A removable strainer or basket shall cover the waste outlet of waste receptors. Waste receptors shall be installed in ventilated spaces. Waste receptors shall not be installed in bathrooms or in any inaccessible or unventilated space such as a closet. Ready access shall be provided to waste receptors. P2706.3 Prohibited Waste receptors. Plumbing fixtures that are used for domestic or culinary purposes shall not be used to receive the discharge of indirect waste piping. Exceptions: 1. A kitchen sink trap is acceptable for use as a receptor for a dishwasher. 2. A laundry tray is acceptable for use as a receptor for a clothes washing machine. I still don't see it. Do you have something like Nolan shows, where the condensate drain line T's into the sink tail piece? Your reference doesn't seem to prohibit that. A receptor is defined as receiving discharge from indirect waste pipe. Indirect waste pipe is defined as a waste pipe that discharges through an air gap into a trap. Certainly what Nolan shows doesn't have an air gap, so I don't see how it's prohibited by the IRC.
Marc Posted August 22, 2013 Author Report Posted August 22, 2013 P2706.1 General. Every waste receptor shall be of an approved type. Plumbing fixtures or other receptors receiving the discharge of indirect waste pipes shall be shaped and have the capacities to prevent splashing or flooding and shall be readily accessible for inspection and cleaning. Waste receptors and standpipes shall be trapped and vented and shall connect to the building drainage system. A removable strainer or basket shall cover the waste outlet of waste receptors. Waste receptors shall be installed in ventilated spaces. Waste receptors shall not be installed in bathrooms or in any inaccessible or unventilated space such as a closet. Ready access shall be provided to waste receptors. P2706.3 Prohibited Waste receptors. Plumbing fixtures that are used for domestic or culinary purposes shall not be used to receive the discharge of indirect waste piping. Exceptions: 1. A kitchen sink trap is acceptable for use as a receptor for a dishwasher. 2. A laundry tray is acceptable for use as a receptor for a clothes washing machine. I still don't see it. Do you have something like Nolan shows, where the condensate drain line T's into the sink tail piece? Your reference doesn't seem to prohibit that. A receptor is defined as receiving discharge from indirect waste pipe. Indirect waste pipe is defined as a waste pipe that discharges through an air gap into a trap. Certainly what Nolan shows doesn't have an air gap, so I don't see how it's prohibited by the IRC. As I read it, there's supposed to be an air gap...unless it's an exception like dishwasher, etc. Marc
SNations Posted August 22, 2013 Report Posted August 22, 2013 I'm also looking at the 2012 Code Check, and under "Condensate Control (AC & Condensing Furnaces)" it says: "May drain to indirect receptor (lav tailpiece, tub overflow)" and under the '12 IRC column it says [local] and under the '12 UMC column it says {312.5&6}. Maybe the plumbers do consider this to be an indirect receptor but it doesn't seem to fit the definition.
SNations Posted August 22, 2013 Report Posted August 22, 2013 As I read it, there's supposed to be an air gap...unless it's an exception like dishwasher, etc. Marc As I read it this section describes the plumbing for an indirect receptor but it doesn't define what needs to be plumbed that way.
Erby Posted August 22, 2013 Report Posted August 22, 2013 I'm sure there are bigger fish to fry than condensate dripping into a sink trap. The condensate water is coming out of the same air that's circulating in your house through the duct system. The same fumes that are coming out of the vents (usually none) may be in the pipe. If the fumes are a problem in the pipe, they're also a problem in the ducts. T The water in the trap under the sink keeps sewer gases from coming back up the sink or condensate drain llne.
Brandon Whitmore Posted August 23, 2013 Report Posted August 23, 2013 I'm pretty positive you aren't using the proper building code......
Jim Katen Posted August 23, 2013 Report Posted August 23, 2013 Your installation is fine. Go here: http://www.iapmo.org/2010%20California% ... r%2008.pdf Read the second sentence from the end.
Steven Hockstein Posted August 23, 2013 Report Posted August 23, 2013 I'm pretty positive you aren't using the proper building code...... I agree unless you are referring to an apartment on the top floor of a house? The IRC is not the right code if you live in an apartment building.
SNations Posted August 26, 2013 Report Posted August 26, 2013 Your installation is fine. Go here: http://www.iapmo.org/2010%20California% ... r%2008.pdf Read the second sentence from the end. Jim,While it's clear that the OP's installation is fine, the last paragraph of the code you posted isn't totally clear to me. Do you think that this code is calling the connection to the tailpiece (like Nolan posted) an indirect connection? If so then I'm not seeing it.
Jim Katen Posted August 27, 2013 Report Posted August 27, 2013 Your installation is fine. Go here: http://www.iapmo.org/2010%20California% ... r%2008.pdf Read the second sentence from the end. Jim,While it's clear that the OP's installation is fine, the last paragraph of the code you posted isn't totally clear to me. Do you think that this code is calling the connection to the tailpiece (like Nolan posted) an indirect connection? If so then I'm not seeing it. No, I think it's just saying that AC condensate can be disposed of by method A, B, or C.
Douglas Hansen Posted August 27, 2013 Report Posted August 27, 2013 A fixture tailpiece is acceptable for an indirect waste. It has an air break (not an air gap) and meets the definition for an indirect waste. In California (UPC land) there is a prohibition on using the tailpiece of a lavatory sink when it is in the same room with a toilet. Jim's link includes the language. Most jurisdictions do not care about it being in a room with a toilet; it is sometimes the only reasonable way to connnect it. California does not use the IRC energy, plumbing, mechanical, fuel gas, or electrical sections; they only use the building portion.
SNations Posted August 27, 2013 Report Posted August 27, 2013 A fixture tailpiece is acceptable for an indirect waste. It has an air break (not an air gap) and meets the definition for an indirect waste. In California (UPC land) there is a prohibition on using the tailpiece of a lavatory sink when it is in the same room with a toilet. Jim's link includes the language. Most jurisdictions do not care about it being in a room with a toilet; it is sometimes the only reasonable way to connect it. California does not use the IRC energy, plumbing, mechanical, fuel gas, or electrical sections; they only use the building portion. Hi Douglas,The first paragraph of the code the Jim posted says, "Indirect waste piping shall discharge into the building drainage system through and airgap or airbreak as set forth in this code." The IRC definition of "indirect waste pipe" is: A waste pipe that discharges into the drainage system through an air gap into a trap, fixture or receptor. So the IRC leaves off the air break part (and also uses two words for "air gap"). Referring to the picture that Nolan posted, that's not what I think of when I envision an air break, because I envision that to mean that the pipes aren't touching at all (overlapping, but not touching). If you say it's an airbreak then I believe you. But it certainly is not an air gap. Right? So the IRC doesn't prohibit Nolan's example, as far as I can tell. Also, I'm not aware of any authoritative requirement (except for the California code that Jim posted) that AC condensate must drain in an indirect manner into the building's drainage system. I've seen the requirement, but not from an authoritative source. Are you aware of any such source, such as the IRC? Do you know if the International Plumbing Code addresses this issue?
Rocon Posted August 28, 2013 Report Posted August 28, 2013 The IRC does not apply you are in a multi-family unit that was most likely built under the CBC (California Building Code), and the CPC (California Plumbing Code). I know it was commonplace in multi-family units before 2004 (could still be) in the city of Los Angeles to allow this. I realize that LA is not your jurisdiction but generally, if it flies in LA then it flies in Pasadena. As far as hazards go if you are getting fumes from a condensate line there is a bigger problem somewhere since the condensate tray below the coils are in the conditioned air stream of your air handler. I do know the downside of this setup is that if there is a condensate ejector pump or a low spot in the condensation line you will hear gurgling when the condensate gets enough head pressure to discharge into the tailpiece. P2706.1 General. Every waste receptor shall be of an approved type. Plumbing fixtures or other receptors receiving the discharge of indirect waste pipes shall be shaped and have the capacities to prevent splashing or flooding and shall be readily accessible for inspection and cleaning. Waste receptors and standpipes shall be trapped and vented and shall connect to the building drainage system. A removable strainer or basket shall cover the waste outlet of waste receptors. Waste receptors shall be installed in ventilated spaces. Waste receptors shall not be installed in bathrooms or in any inaccessible or unventilated space such as a closet. Ready access shall be provided to waste receptors. P2706.3 Prohibited Waste receptors. Plumbing fixtures that are used for domestic or culinary purposes shall not be used to receive the discharge of indirect waste piping. Exceptions: 1. A kitchen sink trap is acceptable for use as a receptor for a dishwasher. 2. A laundry tray is acceptable for use as a receptor for a clothes washing machine.
Rob Amaral Posted August 29, 2013 Report Posted August 29, 2013 This all points to the 'why' of all of this.. 1
Marc Posted December 29, 2019 Author Report Posted December 29, 2019 Post some photos. I don't click links posted by newcomers that I don't know.
Les Posted December 30, 2019 Report Posted December 30, 2019 I deleted the entire post. it was over six years old and just a link dropper.
raymondf32431 Posted January 17 Report Posted January 17 I believe the "why" for an air break is due to the negative pressure than can occur on the condensate line. Such negative pressure, without an air break (or gap), can suck dry the trap, allowing sewer gases to escape. I (a simple DIY homeowner, so not much weigh there) drain into a pump (serving as the air break), and then pump directly from the pump reservoir into the sink/basin's drainage pipe (pre-trap). This is for anyone thinking about using a pump, rather than directly attaching the drainage to their stack.
Steven Jones Posted January 31 Report Posted January 31 The IRC prohibits connecting condensate drains from cooling systems directly into drain lines before the trap to prevent potential introduction of harmful substances or gases. If your top-floor apartment has this setup, it's a violation that could have occurred due to oversight during inspection or non-compliance. This violation may lead to unpleasant odors and the risk of exposure to harmful substances. To address the issue, consult with a licensed plumber to reconfigure the condensate drain system, ensuring compliance with the IRC. If concerned, contact your local building department to report the issue and seek guidance on rectifying it for a healthier living environment. You can also check for expert advice like at Will plumbing.