Those look like Cutler-Hammer CH breakers. The panel cover would have been tan if it had not been painted over.

CH does hve some breaker listed for 2 conductors.

Posted

No ID info. Wait a minute. Still don't know if rated for two. That's my only shot and too small for me to read at the time.

Click to Enlarge
tn_201351203559_Moran5113%20004.jpg

51.32 KB

Click to Enlarge
tn_201351203820_Moran5113%20005.jpg

54.17 KB

Posted

Hack job. CH and SquareD that accept two conductors have a plate under the screw that the wires go UNDER.

In your picture only the bottom two breakers show that, the four breakers above show the ends and the side of the wire. Looks to me like they weren't inserted properly.

Posted

I didn't enlarge the pic but it seems clear that the lower 3 breakers are of a different design that clearly should only have one wire. (and they do)

The upper ones MAY be rated for two but the photo isn't clear enough for me to see the design clearly.

Posted

Hack job. CH and SquareD that accept two conductors have a plate under the screw that the wires go UNDER.

In your picture only the bottom two breakers show that, the four breakers above show the ends and the side of the wire. Looks to me like they weren't inserted properly.

Hack job? The wires can only be installed one way. If they don't go under the screw head, where else are they gonna go? The bottom breaker is likely a two pole.
Posted

CH did not have the same retention clamp as Square D.

I just looked on the truck and the newer CH breakers with the plastic mounting foot are labeled for 2 copper conductors or 1 aluminum. I did not see a label on the older metal foot style.

The clamp is a slightly v-shaped lug with a flat pressure plate.

Posted
The wires can only be installed one way.

Famous last words. For everyone that says that, there are at least 10 creative people who will screw it up.

If they don't go under the screw head, where else are they gonna go? The bottom breaker is likely a two pole.

In the picture right above your post it's pretty obvious that there is not enough contact area on several of the breaker terminations. Others are done correctly (same breaker) and the top breaker has the other style with the hole to insert the wire.

That's all you can see without being there.

Posted

Well heck. There are a couple of awg12 wires on 30 amp breakers so I'll get an electrician in there somehow, maybe. Plus the bad deadfront panel missing twistouts.

Thanks for all the replies.

Posted

Here's one on the left side.

Click to Enlarge
tn_20135121649_Moran5113%20017.jpg

81.22 KB

The second and third breaker down are the style that accept 2 conductors.

I question what he did there - a black and a white on a double 30 amp breaker, OK. Then he added a black to one side of that circuit. That looks like the work of an ignoramus.
Posted

Here's one on the left side.

Click to Enlarge
tn_20135121649_Moran5113%20017.jpg

81.22 KB

The second and third breaker down are the style that accept 2 conductors.

I question what he did there - a black and a white on a double 30 amp breaker, OK. Then he added a black to one side of that circuit. That looks like the work of an ignoramus.

Right. Something foul going on there.

Marc

Posted

I don't know what make breakers these are. Do you think they were made to handle to conductors?

If a breaker is made to accept two wires it should be marked with that information. If it's not marked, it shouldn't have two wires connected to it.

Each of the double taps in your pictures is wrong.

Posted

If a breaker is made to accept two wires it should be marked with that information. If it's not marked, it shouldn't have two wires connected to it.

What if you know that it is complaint? Such as this case?

Each of the double taps in your pictures is wrong.

Sorry, I disagree.

Posted

If a breaker is made to accept two wires it should be marked with that information. If it's not marked, it shouldn't have two wires connected to it.

What if you know that it is complaint? Such as this case?

It cannot be compliant unless it is marked. You can find this rule at 110.14(A). It's not new.

Each of the double taps in your pictures is wrong.

Sorry, I disagree.

Please provide a reference for your claim.

Posted

It cannot be compliant unless it is marked. You can find this rule at 110.14(A). It's not new. ..................

Please provide a reference for your claim.

When I go out to my truck I'll take a pic of a C-H CH breaker for you.

My reference is that I know it from experience.

Posted

It cannot be compliant unless it is marked. You can find this rule at 110.14(A). It's not new. ..................

Please provide a reference for your claim.

When I go out to my truck I'll take a pic of a C-H CH breaker for you.

My reference is that I know it from experience.

Look at the catalogue. The CH115 breakers are the only Cutler Hammer breakers that can accept two wires. They have this information molded onto the side of the case. The double-tapped breakers in the original post are not CH115 breakers.

Download Attachment: icon_photo.gif CHbreakers Catalogue Page.jpg

92.26 KB

Posted

It cannot be compliant unless it is marked. You can find this rule at 110.14(A). It's not new. ..................

Please provide a reference for your claim.

When I go out to my truck I'll take a pic of a C-H CH breaker for you.

My reference is that I know it from experience.

Look at the catalogue. The CH115 breakers are the only Cutler Hammer breakers that can accept two wires. They have this information molded onto the side of the case. The double-tapped breakers in the original post are not CH115 breakers.

Download Attachment: icon_photo.gif CHbreakers Catalogue Page.jpg

92.26?KB

You are reading that catalog page wrong. Those wire specs are for ALL the breakers in that size range; 10-30A. NOT just for 15A.

See how the box you highlighted is as big as all the breaker size in that section?

And please check out these threads where this has been hashed to death already - always with the same outcome:

I don't need those threads for this information. Thanks though.

Posted

It cannot be compliant unless it is marked. You can find this rule at 110.14(A). It's not new. ..................

Please provide a reference for your claim.

When I go out to my truck I'll take a pic of a C-H CH breaker for you.

My reference is that I know it from experience.

Look at the catalogue. The CH115 breakers are the only Cutler Hammer breakers that can accept two wires. They have this information molded onto the side of the case. The double-tapped breakers in the original post are not CH115 breakers.

Download Attachment: icon_photo.gif CHbreakers Catalogue Page.jpg

92.26?KB

Just have to correct that bit, given that it was my highlighting I posted (somewhere?) many moons ago. It's not just the CH115...it's all in that upper box, CH110 thru CH130. The shaded "(2) #14-10" just happens to be on the same line as the CH115, but it applies to all five of those. Also all the 2-pole breakers in the same section (CH210 thru CH230).

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
×
×
  • Create New...