Mike Lamb Posted March 6, 2013 Report Posted March 6, 2013 Could someone please direct me to the reference as to how close the main disconnect should be from where the SEC enters the interior of the house?
Marc Posted March 6, 2013 Report Posted March 6, 2013 230.70(A)(1) (08' NEC) It doesn't prescribe a particular distance. It depends on the mood and character of the particular AHJ on the day the question is put to him. Marc
Mike Lamb Posted March 6, 2013 Author Report Posted March 6, 2013 230.70(A)(1) (08' NEC) It doesn't prescribe a particular distance. It depends on the mood and character of the particular AHJ on the day the question is put to him. Marc That's it. Thanks. I could not remember if there was some required distance. ...either outside of a building or structure or inside nearest the point of entrance of the service conductors....
Shawshill Posted March 13, 2013 Report Posted March 13, 2013 It depends on if it is a feeder or service, different articles pretty much same info. FEEDER 225.31 Disconnecting Means 225.32 Location The disconnecting means shall be installed either inside or outside of the building or structure served or where the conductors pass through the building or structure. The disconnecting means shall be at a readily accessible location nearest the point of entrance of the conductors. For the purposes of this section, the requirements in 230.6 shall be utilized SERVICE 230.70 General Means shall be provided to disconnect all conductors in a building or other structure from the service-entrance conductors. (A) Location. The service disconnecting means shall be installed in accordance with 230.70(A)(1), (A)(2), and (A)(3). (1) Readily Accessible Location. The service disconnecting means shall be installed at a readily accessible location either outside of a building or structure or inside nearest the point of entrance of the service conductors. (2) Bathrooms. Service disconnecting means shall not be installed in bathrooms. (3) Remote Control. Where a remote control device(s) is used to actuate the service disconnecting means, the service disconnecting means shall be located in accordance with 230.70(A)(1).
Rob Amaral Posted March 14, 2013 Report Posted March 14, 2013 yeah.. but an inspector should know 'why' this is the recommendation or rule.... If you know 'why', people salute... including electricians and code officials...
Marc Posted March 14, 2013 Report Posted March 14, 2013 yeah.. but an inspector should know 'why' this is the recommendation or rule.... If you know 'why', people salute... including electricians and code officials... The why is obvious...The utility fuse that protects these conductors is big enough to fry them and put the house on fire. By keeping them short, the risk of something going wrong is minimized. Marc
Jim Katen Posted March 15, 2013 Report Posted March 15, 2013 yeah.. but an inspector should know 'why' this is the recommendation or rule.... If you know 'why', people salute... including electricians and code officials... The why is obvious...The utility fuse that protects these conductors is big enough to fry them and put the house on fire. By keeping them short, the risk of something going wrong is minimized. Marc Just to be clear, the utility fuse *does not* protect the conductors.