MPdesign Posted November 27, 2012 Report Share Posted November 27, 2012 Just to recheck, Is there anything wrong with aluminum wiring being used on devices rated for Cu/Al? No special pigtails or anything - all aluminum. Link to comment Share on other sites More sharing options...
Marc Posted November 27, 2012 Report Share Posted November 27, 2012 CU/ALR, CU/AL More near the end of this article: Creep in older aluminum formulations Marc Link to comment Share on other sites More sharing options...
hausdok Posted November 27, 2012 Report Share Posted November 27, 2012 Hi, Light switches and receptacles should be CU/ALR. Those are designed for the thicker aluminum wiring. The breakers can be CU/AL.. ONE TEAM - ONE FIGHT!!! Mike Link to comment Share on other sites More sharing options...
Jim Katen Posted November 28, 2012 Report Share Posted November 28, 2012 Just for clarity, there's no such thing as a CU/ALR. It's either CU/AL or CO/ALR. Link to comment Share on other sites More sharing options...
hausdok Posted November 28, 2012 Report Share Posted November 28, 2012 You know that's what I meant, right? You're a moderator, you could have corrected it. Just sayin' ONE TEAM - ONE FIGHT!!! Mike Link to comment Share on other sites More sharing options...
Jim Katen Posted November 28, 2012 Report Share Posted November 28, 2012 You know that's what I meant, right? You're a moderator, you could have corrected it. Just sayin' ONE TEAM - ONE FIGHT!!! Mike Well, it's both you and Marc. I'm happy to delete inappropriate posts, but I'd rather not edit others' posts. Link to comment Share on other sites More sharing options...
Recommended Posts
Create an account or sign in to comment
You need to be a member in order to leave a comment
Create an account
Sign up for a new account in our community. It's easy!
Register a new accountSign in
Already have an account? Sign in here.
Sign In Now