Jerry Lozier Posted August 22, 2012 Report Share Posted August 22, 2012 Typically the capacity in tons of a Trane outdoor unit can be determined by dividing the 7th and 8th digit of the model number by 12. Click to Enlarge 39.85 KB Is it ever for the 5th and 6th # which would be a 5 ton????????? Link to comment Share on other sites More sharing options...
Marc Posted August 22, 2012 Report Share Posted August 22, 2012 Yes, to my knowledge. Only Carrier is easily misread. Marc Link to comment Share on other sites More sharing options...
Bill Kibbel Posted August 23, 2012 Report Share Posted August 23, 2012 Trane current/recent models use the 7th and 8th digit. The serial number would start with a 2 or 4 (indicating R-22 or R-410). If it starts with three letters, it's an older model and is decoded as: 1st three digits TWX = heat pump 4th digit 0 = brazed 5th and 6th 60 = capacity - 5 tons. Link to comment Share on other sites More sharing options...
plummen Posted August 23, 2012 Report Share Posted August 23, 2012 Lennox always makes my head hurt trying to figure sizing of condensing units,tranes usually arent to bad just look for a number a combination of 12 or 6 will go into Link to comment Share on other sites More sharing options...
Jerry Lozier Posted August 23, 2012 Author Report Share Posted August 23, 2012 Thanks guys Link to comment Share on other sites More sharing options...
randynavarro Posted August 23, 2012 Report Share Posted August 23, 2012 I've always just looked at the model number and anything close to a number somewhere in the middle of that number that's dividable by 12 is the tonnage. I'm sure there's a unit out there somewhere that doesn't follow that rule, but I haven't seen one in the 3 units I've seen this year. . . the 20 units I've seen in the last 14 years. Link to comment Share on other sites More sharing options...
Terence McCann Posted August 23, 2012 Report Share Posted August 23, 2012 Is the home big enough for a 5 ton unit? Link to comment Share on other sites More sharing options...
Phillip Posted August 24, 2012 Report Share Posted August 24, 2012 Hi Terry, How many Sq. Footage per ton do you use when looking at the size of an unit? Link to comment Share on other sites More sharing options...
Jerry Lozier Posted August 24, 2012 Author Report Share Posted August 24, 2012 3300' 2 story, 1965 home 2x6 walls, vinyls, subfloor insulated, 8-10" blown in attic, dry moderate climate, extremes of 100+ in summer (avg 80's), near zero in winter (avg 30's). Recommended they add attic insulation and baffle soffit vents. Has newer laminate roof with ridge venting. Link to comment Share on other sites More sharing options...
kurt Posted August 24, 2012 Report Share Posted August 24, 2012 1 ton per 750sf is the rough range commonly cited. That'd figure out to about 4.4 ton for this house. So, theoretically, 5 ton might be close. There's a lot to consider in sizing equipment, and there really isn't any standard multiplier that's going to be 100% accurate for all cases. Link to comment Share on other sites More sharing options...
Terence McCann Posted August 24, 2012 Report Share Posted August 24, 2012 Hi Terry, How many Sq. Footage per ton do you use when looking at the size of an unit? On commercial 1 cfm per sq ft with 400 cfm per ton always worked. With older residential 650 cfm per ton is a good rule of thumb - 1600 sf / 650 = 2.5 ton (rounded up). Newer homes are a lot more energy efficient so lower tonnage is expected. I would think that this has been kicked around before here. What I look for is something that seems really out of whack for the structure. A greenhorn in the HVAC field will always oversize thinking that a bigger unit will always be assured of keeping the structure cool. Just my opinion. Link to comment Share on other sites More sharing options...
kurt Posted August 24, 2012 Report Share Posted August 24, 2012 A greenhorn in the HVAC field will always oversize thinking that a bigger unit will always be assured of keeping the structure cool. Just my opinion. It's a good opinion. There was a national study out of the University of Minnesota several years ago that found over 97% of all HVAC equipment was either oversized or undersized. Glazing orientation and type can wildly skew numbers; few take this stuff into account. Link to comment Share on other sites More sharing options...