Phillip Posted August 5, 2012 Report Posted August 5, 2012 I am see a few zone system on new two story homes. Some have a bypass duct and damper. Some do not. I am writing up the lack of the bypass duct and damper. The question I have is there a proper way to use a zone system with out a bypass duct. Something like slowing the fan down. Thanks guys
Terence McCann Posted August 5, 2012 Report Posted August 5, 2012 Sorry for the late responce Phillip. First off I'd call the manufacture to discuss. The VVT/VAV systems I've seen without bypass dampers have an air flow design that follows the fan curve (or rides the fan curve). It may be acceptable not to have a bypass damper depending on the design of the system. Do you know who the t/c system manufacture is?
Phillip Posted August 6, 2012 Author Report Posted August 6, 2012 Hi Terry, The unit and white control box on top of the unit is made by Carrier. I did not look to see who had made the dampers. I know that all the system I have installed in the past had to have an bypass.
Terence McCann Posted August 6, 2012 Report Posted August 6, 2012 Did you get any model numbers Phillip? I still have some folks at Carrier that I know and can give them a call. Let me know.
RSpermo Posted August 6, 2012 Report Posted August 6, 2012 I recently installed a damper and zoned system with a barometric bypass duct from the supply plenum to the return plenum. The bypass duct functions basically on the static pressure in the supply plenum. I took the static pressure and got .55"WC. That was my goal - around .5. I installed 3 dampers and when one zone is called for it goes full open and the other 2 still remain 50% open. So I think the bypass duct may depend on what the dampers do when that zone that is not the primary zone. You also have to ensure that the bypass duct does not put too much cold air back into the return system. By the way I used 800 KwHrs less this July than last (temps about the same - high 90s - 100 all month).
Phillip Posted August 6, 2012 Author Report Posted August 6, 2012 Click to Enlarge 73.19 KB Click to Enlarge 41.62 KB Terry this is all I have the photos of. Thanks for the help
Phillip Posted August 6, 2012 Author Report Posted August 6, 2012 RSpermo the damper and zoned system with a barometric bypass duct from the supply duct to the return duct is what I see in newer system around here
RSpermo Posted August 7, 2012 Report Posted August 7, 2012 Phillip, Have you checked the static pressure in all configurations (different dampers opened and closed)? It may very well be that in the worst case the static pressure is approximately .5"WC.
Phillip Posted August 8, 2012 Author Report Posted August 8, 2012 Phillip, Have you checked the static pressure in all configurations (different dampers opened and closed)? It may very well be that in the worst case the static pressure is approximately .5"WC. RSpermo The items you are talking about is beyond a normal home inspection. It would be something an HVAC Technician would do.
Terence McCann Posted August 8, 2012 Report Posted August 8, 2012 Hi Phillip: If you get a chance to swing by there at all get the make and model of the zone system. I'd be curious to see what their control scheme is.
RSpermo Posted August 8, 2012 Report Posted August 8, 2012 Phillip - Exactly why I went out and earned my Texas HVAC Contractor's license. I can now give my clients a more thorough inspection. By the way taking static pressure only requires a "pitot tube" and a pressure measuring gauge.
Phillip Posted August 8, 2012 Author Report Posted August 8, 2012 Terry I see if I can swing by there.
Phillip Posted August 15, 2012 Author Report Posted August 15, 2012 Hi Terry and everyone else Carrier does make a system where you do not have to have an bypass duct and damper. Here is the info they sent me. I haven't read all of it yet. Download Attachment: uiz01-5pd.pdf 639.31 KB Download Attachment: zone-02dg.pdf 431.09 KB
Terence McCann Posted August 15, 2012 Report Posted August 15, 2012 Thanks Phillip, good to stay in the know.
inspector57 Posted September 28, 2012 Report Posted September 28, 2012 I just had a new construction today with one unit and two zones, upstairs on one zone, downstairs on the other. Most times I also see barometric zone dampers on a bypass duct but not on this one. Each zone damper is either full on or off which means the remaining zone gets the full flow from the blower. The entire system whistled at the return all the time (one central return grill) and the active zone whistled at all registers when the other was off. Just as a general note, I always check zoned systems in all possible configurations to check for this situation. Basically, the builder here tried to cheap out and skip the bypass and got caught. I am calling it out and recommending the installation of a bypass duct and damper. As alluded to by RSpearmo, check your TD to make sure they don't bypass too much air and start making ice on the coil. They could design the duct system large enough to handle all the air on either zone and not have to have a bypass but that is a bit trickier to have it large enough for full volume but still have enough static pressure in all modes.