Is there verse prohibiting a Cat IV PVC vent from being installed inside a clay chimney flue that is venting a Cat I water heater.

Click to Enlarge
tn_2012720215159_033.jpg

51.29 KB

Posted

That's OK. I have to get this report out now.

The installation is questionable. The clay liner was broken about 30" below the crown so that's a problem right there.

Posted

How about this one.

M1801.4 Space Around Lining - The space surrounding a flue lining system or other vent installed within a masonry chimney shall not be used to vent any other appliance.

ONE TEAM - ONE FIGHT!!!

Mike

Posted

I don't like that one Mike - Chapter 18 is basically about oil. Try this one from the chapter on gas-burning appliances:

G2427.5.9 (503.5.10) Space surrounding lining or vent. The remaining space surrounding a chimney liner, gas vent, special gas vent, or plastic piping installed within a masonry chimney shall not be used to vent another appliance.

Posted

Hi Douglas,

Yes, I hadn't thought of that and I think you nailed it with the part that says, "Or plastic piping installed within a masonry chimney."

ONE TEAM - ONE FIGHT!!!

Mike