I can confuse the heck out of myself so Here is my questions-
Sub-panel in a detached garage has a 8-2 with ground as its supply. It is wired as 240 volt
So does it need 1) A ground rod driven
2) Seperated grounds and neutrals
3) A covered neutral
4) should an 8-3 with ground have been ran
The garage does have a sidewalk connected to the house. It does have GFCI protected outlets.
Man I have read Article 250 till I"m blue in the face.
I think it needs a grounding conductor to a ground rod. I think the grounds and neutrals can be together in this instance.
Am I wrong. Help me Obi-Wan.
I know this is probably supposed to be easy but I just don't see it enough to be comfortable.
Buster
PS Hansons book is in the mail.
Download Attachment: icon_photo.gif Yanowski 013.jpg
85.32 KB
The white should be re identified.
The splice on the red should be nutted not taped.
The ground and neutral should be isolated.
3 wire w/ground should have been run to the panel.
The person who wired the panel should be shot for making such a mess of so few wires.
I think Cramer said one time "separate the ground & neutral anywhere after the first main disconnect". Makes it real simple.
If I quoted that wrong, I apologize.
Hi,
It has more than one branch circuit so it requires its own service grounding electrode and conductor. [250-32a] Ideally it should be the steel in the walk between the house and the garage or a metal pipe below grade, but if it's only got a water pipe inside the building available, you need to add a rod.
Remove the green bonding screw. Install a separate ground bus screwed directly to the panel, move the EGC's onto it. Connect the grounding electrode conductor to it and the SGE.
Done.