AHI in AR Posted January 22, 2012 Report Share Posted January 22, 2012 I came across a hollow, relatively light gauge galvanized steel tube used as a grounding rod today. I don't know the actual thickness since the top was distorted due to being mauled by a hammer, but I suspect it was simply a piece of conduit re-purposed for this use. Age about 20 years or so, and rusting pretty heavily at the soil line. Seems fishy at best. I wrote it up for replacement simply due to the rust, (and the likelihood that it wasn't 8' deep) but I'm curious if anyone is aware of any hollow rods that are/were OK? Link to comment Share on other sites More sharing options...
ericwlewis Posted January 22, 2012 Report Share Posted January 22, 2012 this article mentions a hollow grounding electrode but nothing about gauge. http://www.nachi.org/grounding-electrodes.htm like you, I would think it hinky and probably only a few ft deep [:-thumbd] Link to comment Share on other sites More sharing options...
Chad Fabry Posted January 22, 2012 Report Share Posted January 22, 2012 (5) Rod and Pipe Electrodes. Rod and pipe electrodes shall not be less than 2.44 m (8 ft) in length and shall consist of the following materials. (a) Grounding electrodes of pipe or conduit shall not be smaller than metric designator 21 (trade size ?) and, where of steel, shall have the outer surface galvanized or otherwise metal-coated for corrosion protection. (b) Grounding electrodes of stainless steel and copper or zinc coated steel shall be at least 15.87 mm ( in.) in diameter, unless listed and not less than 12.70 mm (? in.) in diameter. Link to comment Share on other sites More sharing options...
Bill Kibbel Posted January 22, 2012 Report Share Posted January 22, 2012 In this area, galvanized steel pipes for the grounding electrode were quite common. A majority that I see are severely corroded. Many times a gentle wiggle will snap it right off. Click to Enlarge 23.32 KB Link to comment Share on other sites More sharing options...
AHI in AR Posted January 22, 2012 Author Report Share Posted January 22, 2012 Thanks for the replies. It may be a regional thing, but I might see one hollow rod for every fifty solid ones. Generally, the hollow ones are on older installations. I always wiggle solid rods to try to gauge whether they are possibly too short, but I don't grab or wiggle the older, hollow ones precisely because I am afraid they might break. On a related note, this pic is of a rod I easily pulled out that was inserted all of 6" deep...and most of that was through gravel. As you can see the total rod length was less than 2'. The home was built in 2002 in a town that does have muni inspections. It appears that the inspector was sleepwalking that day. Click to Enlarge 105.71 KB Link to comment Share on other sites More sharing options...
Jim Katen Posted January 22, 2012 Report Share Posted January 22, 2012 I came across a hollow, relatively light gauge galvanized steel tube used as a grounding rod today. I don't know the actual thickness since the top was distorted due to being mauled by a hammer, but I suspect it was simply a piece of conduit re-purposed for this use. Age about 20 years or so, and rusting pretty heavily at the soil line. Seems fishy at best. I wrote it up for replacement simply due to the rust, (and the likelihood that it wasn't 8' deep) but I'm curious if anyone is aware of any hollow rods that are/were OK? Still allowed today, as Chad pointed out. I believe that they're supposed to be at least 3/4". Link to comment Share on other sites More sharing options...
ericwlewis Posted January 22, 2012 Report Share Posted January 22, 2012 21 might mean mm which would=3/4" id mip? I guess my question would be, Is 3/4" thinwall (EMT?) conduit suitable or should it be rigid conduit? Link to comment Share on other sites More sharing options...
Jim Katen Posted January 22, 2012 Report Share Posted January 22, 2012 21 might mean mm which would=3/4" id mip? I guess my question would be, Is 3/4" thinwall (EMT?) conduit suitable or should it be rigid conduit? I just looked through several old editions of the NEC and they all say pretty much the same thing -- 3/4" pipe or conduit. Your interpretation is as good as mine as far as EMT vs RMC etc. Link to comment Share on other sites More sharing options...
Jim Port Posted January 23, 2012 Report Share Posted January 23, 2012 EMT is a classified as tubing. Rigid conduit is considered pipe. Link to comment Share on other sites More sharing options...