Trying to remember. Think I recall seeing a discussion where someone discussed the requirement for a minimum 1ft height from the collar before the exhaust vent on a furnace or water heater is permitted to turn. Anyone recall that discussion or know what the code cite, if any, was?

ONE TEAM - ONE FIGHT!!!

Mike

Posted

2006 IRC: G2427.6.1 (503.6.1) Installation, general.

Gas vents shall be installed in accordance with the terms of their listings and the manufacturer's instructions.

From the Duravent Installation Manual, page 5

8. Connector Rise. plan a minimum of one

foot vertical connector rise coming out of each

appliance

Marc

Posted

I have never saw a problem either. But I always defer back to the manufacturer. Codecheck Complete page 168 in Fig. 50 shows 2 feet just for your FYI.

Click to Enlarge
tn_20111022164722_Codecheck%20p.%20168.jpg

50.71 KB

Posted

I called this one for repair. I thought it looked like there's been backdrafting. A gas guy said it was fine.

Click to Enlarge
tn_2011102301058_tank1.jpg

40.8?KB

Click to Enlarge
tn_2011102301117_vent1.jpg

37.55?KB

Correction - It is flame rollout. Thanks, Rob and Tim. Gas guy said it's ok.

Posted

Everything that I have seen so far makes reference to a minimum one foot connector rise for two or more appliances. I have not see anything related to one appliance all by itself.

See Table G2428.3 (1) or G2428.3(2) in the 2006 IRC. Even DuraVent makes reference to "plan a minimum of one foot vertical connector rise coming out of each appliance" This would indicate to me two or more appliances.

However, I have never seen a problem in my area either way.

Jeff Euriech

Peoria Arizona

Posted

Everything that I have seen so far makes reference to a minimum one foot connector rise for two or more appliances. I have not see anything related to one appliance all by itself.

See Table G2428.3 (1) or G2428.3(2) in the 2006 IRC. Even DuraVent makes reference to "plan a minimum of one foot vertical connector rise coming out of each appliance" This would indicate to me two or more appliances.

However, I have never seen a problem in my area either way.

Jeff Euriech

Peoria Arizona

Those are good points. I'd like to hear Bob Harper's response.

Posted

There seems to be no backdrafting at the draft-hood... that scorching at the burner compartment area could be a case of flame roll-out? (Burner-related problem?)

Or the inside burner compartment shield not in place. I see that one often because some are kind of difficult to get in place so they just lean it up or leave it off.....

Posted

I think it's a "standards typo". It could say "any appliance", or "all appliances".

It's not entirely clear, but I always thought it was indicating individual appliances.