Remoldel on older home, switched previous main panel to sub panel off new main panel. Old 200 amp main (now just a disconnect) they ran #2 AL with a 70 amp breaker in new main panel.

QUESTION: any reason the old (now subpanel) should not have been rewired with neutrals floated as they are bonded like a main panel.

old panel

Click to Enlarge
tn_2011104185146_PA040096.jpg

34.32 KB

#2 AL from new panel

Click to Enlarge
tn_2011104185222_PA040099.jpg

41.78 KB

70 amp breaker in new panel to sub

Click to Enlarge
tn_2011104185244_PA040101.jpg

47.95 KB

Grounds and neutrals bonded

Click to Enlarge
tn_201110418538_PA040102.jpg

58.88 KB

thanks guys

Posted

The sub panel enclosure should be bonded to the equipment grounding bus bar and not the neutral bus bar. The neutrals in the sub panel should be on a bus bar that is entirely separate from the one for the EGC's.