John Dirks Jr Posted September 21, 2011 Report Posted September 21, 2011 In the picture you'll see the high side line squashed. It still had some flow capability but I'm sure its reduced. I had no problem with standard wording in writing this up. However, I would like to know from technical standpoint, what exactly will happen in this case which could lead to problems? Click to Enlarge 45.07 KB Click to Enlarge 76.98 KB
Marc Posted September 21, 2011 Report Posted September 21, 2011 Liquid refrigerant expands into a gaseous state when the pressure is reduced to the flash point of the liquid. This happens by design at the expansion valve, capillary tube or whatever restriction device is installed. With this squashed liquid line, some pressure drop likely occurs across it. If the pressure drop is sufficient, some of the liquid may flash into a gas, which reduces the amount of liquid refrigerant available to the restriction device and the overall tonnage available to cool the house. If flashing occurs at the squash point, you'll be able to feel the line become cold at the squash point. In more severe conditions, ice will build up. The squash might also increase the possibility of liquid flashing at some other point between the squash point and the restriction device with the same detrimental effects. It's more likely to flash when ambient temperatures are higher, which means the detrimental effect of the squash is highest on days when cooling is most needed. Marc
rkenney Posted September 21, 2011 Report Posted September 21, 2011 Evaporator starvation Evaporator icing Low/no airflow (blower) Insufficient cooling High compressor pressures (discharge) Low suction pressure Ultimately Compressor failure Same end result as a low refrigerant charge.
Recommended Posts
Create an account or sign in to comment
You need to be a member in order to leave a comment
Create an account
Sign up for a new account in our community. It's easy!
Register a new accountSign in
Already have an account? Sign in here.
Sign In Now