Is this Al wire ok in this breaker terminal?

It looks like it's too large. Is that a #6 conductor? The largest you can use is #8. If it's #8, you're supposed to put all of the strands under one side of the saddle, not split them up.

Do the markings on the breaker imply solid conductor wire only?

No. Solid or stranded is fine.

Posted

What Jim said.

Also - The markings in your first photo indicate that aluminum wire is acceptable. The "SWD" in the first photo means "switching device" meaning that the prototype of this breaker is also listed for use as a switch for fluorescent lighting.

Posted

Hadn't noticed when looking at this type of breaker before but it seems to indicate that you can only use one AL wire even though you can use two copper wires.

Posted

Thank you so far.

The circuit is a 120v supply for the natural gas range. One can see the empty breaker below the top one in the pic--the original intention was to have a 240v electric range.

I couldn't i.d. the exact wire size. Anyone have good tricks for that if there's no visible marking on the cable?

Douglas--see you this weekend in Seattle at the ASHI WW seminar.

Jim--you going?

Anyone else going?

Posted

Hadn't noticed when looking at this type of breaker before but it seems to indicate that you can only use one AL wire even though you can use two copper wires.

I believe that is correct - only one Al, and if you do attach two copper, the max wire gauge drops to #10.

Randy, I agree it is pretty hard to estimate wire size by just looking sometimes.

In this example, you would expect #8 Cu for a 40 amp range circuit. From that, I would deduce that Al to be a size larger - #6.

Posted

What about incandescant lighting?

The SWD rating is an additional (and pretty meaningless) designation. It can also be used as a switch for other purposes, such as incandescent lighting.

I think the idea is that an older magnetic-ballast fluorescent has a greater initial current surge, and the SWD rating means that UL has evaluated it for a certain number of such operations without degradation of the internal contacts.

Posted

Thank you so far.

The circuit is a 120v supply for the natural gas range. One can see the empty breaker below the top one in the pic--the original intention was to have a 240v electric range.

I couldn't i.d. the exact wire size. Anyone have good tricks for that if there's no visible marking on the cable?

Fetch yourself over to Ohm Depo and buy 2" lengths of each size of cable.

Douglas--see you this weekend in Seattle at the ASHI WW seminar.

Jim--you going?

Anyone else going?

I'm still trying to clear my schedule, but I'll try to be there.

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
×
×
  • Create New...