JohnC Posted August 27, 2011 Report Posted August 27, 2011 Can the gas line be run up the basement ash pit? I have never seen it done before. Thanks John Callan Click to Enlarge 32.19 KB Click to Enlarge 34.52 KB Click to Enlarge 50.71 KB
Hearthman Posted August 27, 2011 Report Posted August 27, 2011 Not a problem in an of itself but you have several huge issues hidden in there. -There is an exposed gas vent connector rotted through leaking combustion fumes. This should be encased in a masonry sleeve or B-vent then attach properly to the terra cotta heater flue. The heater flue must be separated from the fireplace by a nominal 4" wythe wall meaning you should never be able to see the heater flue from an ash pit. -you have combustible plywood forms under the hearth. It all must be torn out and rebuilt. This is a major expense to repair! That heater can kill someone and should have been shut down and red tagged on the spot. I strongly suggest you call the Realtor immediately then send a Certified letter return receipt informing them of the hazard and consequences.