Posted

There are 2 conductors under the large lug at the top of the grounding/neutral bar on this Cutler Hammer panel. Is that lug rated for more than one conductor? The photo is as close as I could get.

The black conductor is the neutral to a sub panel, I've called that out.

Thanks

Click to Enlarge
tn_2011425184520_P4250020%20copy.jpg

54.81 KB

Posted

There are 2 conductors under the large lug at the top of the grounding/neutral bar on this Cutler Hammer panel. Is that lug rated for more than one conductor? The photo is as close as I could get.

The black conductor is the neutral to a sub panel, I've called that out.

Thanks

Click to Enlarge
tn_2011425184520_P4250020%20copy.jpg

54.81 KB

The lug is almost certainly not rated for two wires. If it were, there'd be a marking on it to that effect.

Posted

Thanks Jim. I wanted to make sure. This was a re inspection. I had called this out the first time, but this and other items in the panel were not corrected, no surprise.