John Dirks Jr Posted March 25, 2011 Report Posted March 25, 2011 This can be found in the Gastite installation manual. This is from page 48 of the Gastite Design and Installation Guide November 2008- Care should be taken when installing vertical runs to maintain as much separation as reasonably possible from other electrically conductive systems in the building. I would like to find similar language but in Omegaflex TracPipe manual. I've been looking for a while now. Do any of you know if similar language is in the TracPipe manual? If so, where? Thanks.
John Dirks Jr Posted March 27, 2011 Author Report Posted March 27, 2011 The furnace that feeds these ducts has a metal flue that goes through the roof like a lightning rod. Click to Enlarge 30.94 KB
gpdewitt Posted March 27, 2011 Report Posted March 27, 2011 Article 250 of the NEC has grounding/bonding requirements that apply to both CSST and ducts, if that helps.