EricS Posted March 21, 2011 Report Posted March 21, 2011 Saw a sub panel back fed by a 100amp breaker in the main. The common from the sub and common from the main where clamped togther in the main panel. Is this okay? I ask because we came across serveral outlets powerd by the sub that were not reading a ground. Could the two commons being together cause a false read? Thanks Eric
hausdok Posted March 21, 2011 Report Posted March 21, 2011 When you refer to "commons" are you referring to the equipment-grounding conductors ("grounds" - bare or green wires) or to the grounded conductors ("neutrals" - white wires)? ONE TEAM - ONE FIGHT!!! Mike
hausdok Posted March 21, 2011 Report Posted March 21, 2011 OK, Now I think I'm forming a picture; the grounded (neutral) conductor from the sub-panel is secured under the same lug in the main panel as the grounded conductor from the service entrance. As far as I know, it's not OK to do that. First, a lug has to be rated for two conductors and second there is rule that grounded conductors will each have their own little seat on the bus. There should have been another lug somewhere on the neutral bus in that main panel to which the grounded conductor from the sub-panel feeder can be attached. ONE TEAM - ONE FIGHT!!! Mike
John Kogel Posted March 22, 2011 Report Posted March 22, 2011 The grounding or lack of it should not be related to the doubled neutrals except for one thing - both are signs of amateur attempts at wiring. I'd call for a qualified electrician to inspect the whole setup.
Recommended Posts
Create an account or sign in to comment
You need to be a member in order to leave a comment
Create an account
Sign up for a new account in our community. It's easy!
Register a new accountSign in
Already have an account? Sign in here.
Sign In Now